In Part 4, the delta-T (change in temperature) is calculated from the start temperature to the maximum temperature. For instance, a material having a start temperature of 748degC and the maximum of 800degC will be considered a failure, although it could be a practically inert product. However, in Part11 the delta-T is the difference between the maximum to end temperature and, hence, in my opinion, this is a less onerous test. Besides, there are differences between the furnaces such as the density of the packing materials.
In part 4, the duration of the flaming is limited to a maximum of 10s. On the face of it, this may seem less onerous, but if the product flames for a period of, say, 5s then the temperature will in all likelihood rise more than 50degC. In Part 11 the requirement is ‘no flaming’, but the definition is no sustained flaming for more than 5s. One could have flashes of fire throughout the test lasting less than 5 seconds, but it will not be recorded as ‘flaming’.