I am wondering if those of you out there would mull over the following and provide feedback on my argument for the removal of this block of flats AOV?
I recently assessed a block of flats that's structure consisted of:
3 storey;
2 flats per floor, each with internal lobby and 30 minute fire resisting final exit door (protected staircase) including intumescent strips, cold smoke seals and self closer;
Purpose built - late 80's by reputable local developer;
mainly non-combustible;
single enclosed staircase with no externally openable windows;
AOV in ceiling of stair; likley to have been requirement of CP3/BS5588 at time of build. Cannot confirm this from BC as archives disgarded after 15 years. AOV currently non-serviceable.
Common area compartmentation between flats and stairway is uncompromised - concrete block with render;
Soundness of compartmentation inside flats for above and below unknown - however; beam and block construction and well looked after block without obvious signs of neglect in a fairly affluent location.
Fire strategy - Stay put.
The residents are keen not to incur any unnecesary maintenance costs - in particular to fire safety, the servicability of the AOV.
Taking into account the following points I believe it is reasonable to consider that the AOV be removed:
- Based on the design and materials used in this building's construction I believe it is reasonable to consider that the fire strategy (stay put) is correct;
- As adequate protection has been provided to the staircase it is unlikely that copious amounts of heat and smoke will disperse into it/li]
- With consideration of the adopted stay put policy the staircase is not needed for escape;
- Although access cannot be made to each flat it is of my view that it is reasonable to consider from the materials used in construction that compartmentation is and will remain sound
what do your alls reckon and based on the previous thread's comments by jokar that the FRS are being prescriptive opposed to risk based is there any point in taking the argument to them anyway?
Not sure if anyone out there has the statistics but another thought was on how many occasions over the past so many years has it been necessary that AOV be activated so as to prevent injury or loss of life. This stat alone could if weighted on the wrong side of safety disslove my argument immediately; however; if its one in a million maybe I could use it as further argumentable weight.