Mind Block
« on: January 23, 2011, 11:02:13 AM »
1. In a ground and first floor public assembly public building with two protected staircases, there is a large room on the first floor.  One set of outward opening double doors leads to one of the protected staircases and, likewise, the other set of outward opening double doors leads to the other protected staircase.  At the base of each staircase there are two separate final exits thereby making a total of 4 final exits.  Each final exit is a single inward opening door (750mm).  If one staircase is lost for fire, are we saying that the other staircase accmmodates 120 people (60 per inward opening door)?
Some people are like clouds. When they disappear it's a brighter day.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Mind Block
« Reply #1 on: January 24, 2011, 07:00:29 AM »
Consider this. If the occupancy factor was 60 and there was one inward opening final exit door, it would be acceptable. If you increased the occupancy to 120 and provided another inward opening door has the situation been made any worse?
If your room was split in two with an occupancy factor of 60 and each having the protected route to the final exit with an inward opening door, would they each be acceptable? Why does removing the seperation between each suddenly create a condition which requires the discounting of one of the exits?
« Last Edit: January 24, 2011, 08:25:59 AM by nearlythere »
We're not Brazil we're Northern Ireland.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Mind Block
« Reply #2 on: January 24, 2011, 09:14:04 AM »
The guidance gives a range of solutions to common everyday situations, your situation does not fall into this category. So it is necessary to consider why the rule about the direction of opening was made - the potential hazards that are well understood and how those hazards can be controlled in this particular case.

The UK guidance is much less prescriptive than the EU Directive, the 50 /60 person guidance for inward opening doors is a UK thing, the directive states that all exits shall open in the direction of escape.

The hazard of an inward opening door is magnified in an assembly building. Could these hazards be realised in this particular case? Apply the guidance and turn the doors or reduce the numbers is the simple answer. However if you cannot change the doors or the numbers of persons then you need to evaluate the hazard and risk.

Are there other factors that could eliminate or mitigate the risk of persons being trapped behind the closed doors? Is there a good distance between the final exits, are they well separated, how will the flow of people down the staircase be controlled, where are the pinch points, what is the width of the staircase,  how much space is there between the base of the staircase and the doors, how is the evacuation managed and controlled, how soon after the raising of the alarm will people arrive at the exits and at what rate will they arrive?

It may be possible to construct an argument for retaining the status quo taking the above points into consideration. But I would go for turning the doors if you can. That way you have an answer that will always work.