A chap called Todd has written a book on the subject of fire alarms-"the Design, Installation, Commissioning, and Maintenance of Fire Detection and Alarm Systems" and his advice is as follows:
"The areas in which detectors should be sited will be defined by the category of system, which in turn, should be such as to meet the specified fire safety objective. Having decided the areas that are to be protected, other than in category L4, L5 and the two systems, a fire detector should be sited at the top of any shaft or enclosure that penetrates through ceilings. In addition, on each floor, a detector should be sited within approximately 1.5 m of the penetration. Even in the case of category L5 or P2 systems, the code suggests that the need for detectors in these positions should be considered at the design stage."