Author Topic: Is a protected route required?  (Read 4245 times)

Offline JC100

  • Full Member
  • ***
  • Posts: 126
Is a protected route required?
« on: February 08, 2012, 08:43:48 AM »
Hi all, wonder if you could help.

A 3 storey residential property is split into two blocks, one containing 4 units and the other 9 units. In the larger block, with 3 units per floor, there is a protected staircase. In the smaller block, there are 2 flats on the 1st and 2nd storey only but no staircase protection is provided; the ground floor is purely for access. The property was built in 1995 as far as i can find. Any ideas why this might be, is a protected stair not required if only 2 units per floor and if so, where can i find information on this?

Thanks

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Is a protected route required?
« Reply #1 on: February 08, 2012, 09:15:11 AM »
See the footnote to paragraph 2.19 on page 26 of ADB B1 2006.

You need to quote the 2001 version, I believe the content is the same but IIR the numbers might be different.

« Last Edit: February 08, 2012, 09:21:40 AM by kurnal »

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: Is a protected route required?
« Reply #2 on: February 08, 2012, 10:19:51 AM »
See also pages 88 and 89 of the purpose built flats guide issued last August, it provides the ADB benchmark and relaxations for small single stair blocks.

Offline JC100

  • Full Member
  • ***
  • Posts: 126
Re: Is a protected route required?
« Reply #3 on: February 08, 2012, 03:01:31 PM »
Thanks for your help.