In warehouses what distance should stock be stored from sprinkler head?
A question I was asked but don't have an answer other than point to the relevant standard even though its not about installation, but where to stack the pallets.
When you say that this is a matter of
"where to stack the pallets", do you mean that someone is stacking pallets in an area that does not have a sprinkler installation that was specifically designed for such storage? Pallet storage has its own guidance. When kurnal says that the storage of idle pallets is
"very high risk", what he means is that they possess a high fire load in a configuration that will accommodate very rapid fire development. This is why they need a lot of water and why a sprinkler system that is not designed to meet the needs of the situation may not be able to contain a fire.
TB215 addresses the issue and Table 2 of 12845 gives max height of sprinkler deflector plates above the top of the stock. Otherwise at least 1m clearance as kurnal says.
Stu