At the moment I think the options are: 1. Brick up the doorways and remove the fire alarm system 2. Seek assurance from the AI that it complies with ADB with the justifications from the deviation from clause 2.21(d) of ADB
William,
Based on the information provided, I do not believe that option 2 above is viable. No matter what the AI says to try and justify the layout it is not his life that is going to be on the line at 3 in the morning when one of the cars catches fire.
As there are two doors I shall assume there are two garages (though it doesn't make much difference). Either these garages:
1. are deemed to be 'car parks', or
2. are ancillary accommodation, or
3. are not deemed to be car parks and they belong to some other property and are independent of the flats.
If 1, then they are not allowed the doors and will have to block them up.
If 2, then they must have ventilated lobbies, as kurnal and TMM have stated, and I would recommend heat detection in the garages linked to the flats.
Item 3 is not a feasible argument for the developer because if they were independent then there would be no requirement for the doors. The presence of the doors makes them, by definition, ancillary to the flats.
Unless there is case law on this to the contrary, I would deem these garages to be covered car parks and not allow the doors.
Threaten a prohibition notice on those parts of the building that fall under the RR(FS)O if the building is not constructed to your satisfaction. That should make them sit up.
Stu