Thanks for your help. there is also a copy of a similar report with the same title available for download on the NIST site.
I am in the middle of an argument between a client and his insurer, the insurer is insisting that the vents be switched to manual and fusible links be changed to 30 degrees above sprinkler bulb temperature, the fusible links are currently are set to 68 deg same as the heads.
Whilst the vents can fairly easily be converted to open when the pumps cut in, changing the fusible links on 150 vents is not so easy.
As I read the reports the fusible links will be a less critical issue and worth arguing over. If the vent is over the fire, fusible link operation is unlikely to delay operation of sprinkler. If the vent is not over the fire the sprinklers are bound to operate first.