Author Topic: Care home with rented accomodation  (Read 3892 times)

Offline Paul2886

  • Full Member
  • ***
  • Posts: 178
Care home with rented accomodation
« on: November 13, 2014, 05:49:08 PM »
Hi, Can I have your thoughts please.
I have visited a care home which has a second floor purely used for 6 rooms where each is used by staff a member as living accommodation. They share a kitchen in a dead-end corridor and currently use the landing as a 'lounge'. It is accessed by a single staircase with a designated fire exit on the first floor at the base of the staircase. My question is where does this all fit in regarding the RA for the home and to whether the LA should have an interest in this sort of HMO arrangement. Sure you may need to some info to give an accurate opinion...cheers

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Care home with rented accomodation
« Reply #1 on: November 13, 2014, 06:54:11 PM »
Do the staff live there all the time or as a fill in between shifts?

Offline Paul2886

  • Full Member
  • ***
  • Posts: 178
Re: Care home with rented accomodation
« Reply #2 on: November 13, 2014, 08:28:10 PM »
Hi Kurnal, No its their permanent living accommodation
« Last Edit: November 13, 2014, 08:46:21 PM by Paul2886 »

Offline wainy1

  • Newbie
  • *
  • Posts: 18
Re: Care home with rented accomodation
« Reply #3 on: November 18, 2014, 08:43:02 PM »
Hi Paul
From the details you have provided, I would treat the staff accomodation as a HMO. The Fire Safety order will apply to the common areas including the communal lounge and kitchen with the bedrooms separated by a minimum of 30 minutes fire protection. With regard to the remainder of the premises being used as a care home; the premises should have a L1 fire alarm system. The risk assessment should cover the care home, the communal areas of the staff accomodation and ensure the fire resisting construction between the staff accomodation is adequate with detection provided within the staff bedrooms.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Care home with rented accomodation
« Reply #4 on: November 18, 2014, 08:49:09 PM »
I would hope that the staircase discharges into a protected area at first floor level. What are travel distances like?

Offline Paul2886

  • Full Member
  • ***
  • Posts: 178
Re: Care home with rented accomodation
« Reply #5 on: November 19, 2014, 06:49:01 PM »
Hi again,
The single staircase from the staff living area discharges onto an external fire escape at first floor level. At the foot of the stairs there is a small protected lobby which gives access, via a push bar, to a final exit door. It also has one residents room off of the same lobby. The travel distance from the furthest point to the head of the stairs, accessed by a fire door, is about 14 metres and to the final exit, mentioned above, probably about 20 metres.
It may sound a bit sketchy at present as have not done an in-depth assessment as yet. Spoke to the local council today who implied they may have an interest in the staff quarters as it seems to be an HMO.