Author Topic: Tenants' Association Offices In High Rise Block  (Read 4317 times)

Offline Tadees

  • Full Member
  • ***
  • Posts: 122
Tenants' Association Offices In High Rise Block
« on: February 03, 2015, 03:06:16 PM »
I assume there would be purpose group separation (60 minutes FR) between tenants' association office in a block and the rest of the block.  Where in Approved Document B can I find reference to this?  I have looked but can'e seem to see it.
Some people are like clouds. When they disappear it's a brighter day.

Offline Messy

  • Sr. Member
  • ****
  • Posts: 343
Re: Tenants' Association Offices In High Rise Block
« Reply #1 on: February 03, 2015, 07:23:27 PM »
Try 8.11   

Parts of a building that are occupied mainly for different purposes should be separated from one another by compartment walls and/or compartment floors. This does not apply where one of the different purposes is ancillary to the other.

Refer to Appendix D for guidance on whether a function should be regarded as ancillary or not.


Offline Tadees

  • Full Member
  • ***
  • Posts: 122
Re: Tenants' Association Offices In High Rise Block
« Reply #2 on: February 05, 2015, 09:49:12 AM »
Thank you.
Some people are like clouds. When they disappear it's a brighter day.