Author Topic: Not testing emergency lighting  (Read 15672 times)

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Not testing emergency lighting
« Reply #15 on: February 13, 2015, 06:49:17 PM »
One should never try to "risk assess away" practices that are industry recognized standards.  That does not mean that failure to follow the practices are an offence though.
Colin Todd, C S Todd & Associates

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Not testing emergency lighting
« Reply #16 on: February 13, 2015, 11:02:23 PM »
I would suggest that depends on the standard. I regularly risk assess away elements of  BS 5306-8, BS9991, BS9999, BS9990 and some of the recently issued LPC sprinkler tbs are becoming targets too.  And the risk assessment can work both ways - sometimes the benchmark is too low. In my humble opinion of course.

Offline idlefire

  • Jr. Member
  • **
  • Posts: 97
Re: Not testing emergency lighting
« Reply #17 on: February 14, 2015, 04:31:46 PM »
Never say "never" Colin.

I recall a few years ago, as an enforcing authority under the FSO, inspecting a premises where the responsible person had bespoke white fire alarm manual call points made so that they wouldn't contrast with the colour of the walls; the fire risk assessment managed to convince me that this derigation from standard was actually reasonable in the circumstances (I still have the photos).

The same responsible person had bespoke gold mcps in other premises and I was led to believe that you had personally risk assessed one such premises.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Not testing emergency lighting
« Reply #18 on: February 16, 2015, 11:53:25 PM »
That is all cop stuff, not industry standard maintenance practices.  You missed the point.
Colin Todd, C S Todd & Associates

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: Not testing emergency lighting
« Reply #19 on: February 20, 2015, 11:01:57 AM »
One should never try to "risk assess away" practices that are industry recognized standards.  That does not mean that failure to follow the practices are an offence though.

Absolutely on the mark!