Dave,
Assuming Part 6 and a fire alarm system within the flat, rather than protecting the common parts.
The Electrical supply should be part of the Residents Supply, but should not be connected via a keycard meter. If a panel is included, i.e. Grade A, B or C, then a dedicated supply to the equipment, and not through a common RCD. Local Isolation adjacent to the Panel.
If it is a system without a Panel, i.e. Grade D (Mains Smoke Alarm with Battery Back Up), then it does not have to be a dedicated circuit, (although encouraged), but can be supplied from local lighting circuit, which actually assists as the user is more likely to become aware if the circuit has failed.
I will never install a Grade E (Mains only, no Battery Back up) system, so no likelihood of that ever becoming an issue.
Happy to be corrected, and I know I have simplified it, but I am a simple man.
Bill