Quick one - what exactly constitutes a C grade system???I know what the components are (as per 5839:Part 6) but what achieves it other than a Part 1 component system?

Graeme

  • Guest
NHS Supported HMO -Query
« Reply #1 on: May 24, 2006, 10:17:49 PM »
The difference is that smoke alarms are linked to central control equipment not control and indicating equipment.

which i assume is something like a remote hush and test switch or similar

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
NHS Supported HMO -Query
« Reply #2 on: May 25, 2006, 07:17:53 AM »
"Grade C: A system of fire detectors and alarm sounders (which may be combined in the form of
smoke alarms) connected to a common power supply, comprising the normal mains and a
standby supply, with central control equipment."
This sounds to me more like a PSU supplying the power to the heads, as opposed to a grade D system which has mains with internal battery back up.
However,I've just checked annex B which states -
"B.5.1 More effective control and monitoring of a fire detection and fire alarm system can be provided by
connecting all fire detectors to a common power supply, comprising the normal mains, rectified and
regulated as appropriate, with a standby supply, such as a secondary battery. Examples of such systems
include:
a) one or more smoke alarms and heat alarms operating at extra-low voltage and connected to a control
unit at an appropriate location in the dwelling;
b) intruder alarm systems or social alarm systems that incorporate control and indicating equipment to
which one or more fire detectors are connected; the detectors can be smoke alarms or fire detectors with
independent sounders.
B.5.2 This type of system normally incorporates a secondary battery of a type unsuitable for use in normal
domestic appliances and removable only with the use of a tool. The battery is, therefore, unlikely to be
removed for other purposes"
So, in reading this it's either a fire panel stuck in a meter cupboard somewhere (which explains a few things that I've came across) or an intruder panel (Arghhh!!!) with detection on it.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
NHS Supported HMO -Query
« Reply #3 on: May 25, 2006, 02:51:54 PM »
Must be my age - getting the picture now!! http://www.brk.co.uk/index.php?fuseaction=prod.flexi

Graeme

  • Guest
NHS Supported HMO -Query
« Reply #4 on: May 25, 2006, 06:20:10 PM »
Flexipoint provides a Grade C system as defined by BS5839 Part 6. It comprises smoke detectors and alarm sounders connected to a common mains power supply, with battery back up in all units with an element of central control.


kinda similar to wot i said Buzz ;)

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
NHS Supported HMO -Query
« Reply #5 on: May 25, 2006, 06:48:28 PM »
Ahhhh shaddapp!!

Graeme

  • Guest
NHS Supported HMO -Query
« Reply #6 on: May 25, 2006, 07:25:36 PM »
like you say mate-it could be your age.

i'm still a young upstart and have it all to come one distant day... :D

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
NHS Supported HMO -Query
« Reply #7 on: May 26, 2006, 04:55:26 PM »
In the words of Columbo "Just one more thing?" - For a grade C is it detection throughout or just in areas of circulation??
I must read up on things!!For reference - NHS occupied HMO + LD1 (Grade C)!!

Graeme

  • Guest
NHS Supported HMO -Query
« Reply #8 on: May 26, 2006, 05:44:04 PM »
Buzz

LD1
Throughout with all circulation areas that form an escape route and in all areas where a fire might start other than shower rooms,toilets and bathrooms.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
NHS Supported HMO -Query
« Reply #9 on: May 26, 2006, 08:46:58 PM »
Quote from: Graeme Millar
Buzz

LD1
Throughout with all circulation areas that form an escape route and in all areas where a fire might start other than shower rooms,toilets and bathrooms.
I know that now!!!I just missed it first time I read through it!

Graeme

  • Guest
NHS Supported HMO -Query
« Reply #10 on: May 26, 2006, 10:11:25 PM »
well you did ask mr Grumpy