Thanks Fishy, Guess who got a letter from the fire service today, (a copy to the owners of the above mentioned building), it read; (cutting out the in-betweeny bits)
Notification of Deficiencies,
Further to the recent visit carried out on **/**/2006 the fire authority is in the opinion that you are not fully complying with the above legislation, (regulatory reform (fire safety) order 2005
blah blah blah.....you are strongly advised to obtain the appropriate "Fire Safety - Risk Assessment publication for your premises, blah blah.....
REPORT
Deficiency from article 9 (1)
The fire Safety risk assessment was not suitable and sufficient
REMEDY, blah blah.... "you guys know the wording"
Deficiency from article 9 (3)
The F.S.R.Assessment has not been reviewed on a regular basis
REMEDY, "ditto"
Deficiency from article 11 (2)
The F.Safety arrangements for the effective planning, organisation, control, monitoring and review of preventative and protective measures have not been recorded where appropriate,
REMEDY, The responsible person must record F.S Arrangements......blah blah...
a) He employes five or more employee;
b) A licence under an enactment is in force in relation to the premises; or
c) An alterations notice requiring this is in force in relation to the premises.
(this bit above "b" anc "c" Im not to sure what it means, so if anyone can post the answer, that would be great)
and finaly
Deficiency from Article 14 (2)(g)
The escape routes were not provided with adequate signage.
REMEDY, Suitable and sufficient signage indicating all emergency routes and exits is to be provided.