Thanks for your responses.
The new draft Part B further confuses things because it states that.... 'apartment buildings with a floor more than 30m above ground level should be fitted throughout with a sprinkler system in accordance with BS9251'.
Some respondents to this version of Part B identified that 'BS9251 limits its scope to buildings up to 20m in height with the effect that a conventional (commercial) type sprinkler system should be used above this height'. Presumably they mean that it should be designed to 5306/12845.
9251 states... ‘where buildings exceed 20m in height, special circumstances need to be considered and the authority having jurisdiction should be consulted. This matter is receiving the attention of the relevant BSI committee with a view to issuing an amendment’.
1 -------- Does anyone know whether the BSI have got anywhere with this?
9251 does show schematics with pumps installed. So the 20m doesn't appear to tie in with the limit of available mains pressures. 9251 requires the pipework to be hydraulically calculated.
2 -------- On this basis would it be reasonable to suggest that a system could be designed in line with 9251 flow and pressure requirements and broken into vertical zones (up to a maximum of 45m per vertical zone, as per BS5306) and fitted with a multi-stage pump where the building is over 45m in height?
Further comments would be appreciated.