Off topic I know - how many addressable spurs can you put on a loop??Customer wants to upgrade around 12 conventional zones (circa 14 devices/zone) to addressable using existing wiring (future rocky so wants to bring it up as best they can).I have only done it in large computer rooms where there has previously been a 4 + 2 conventional.
Technically, you could in theory have as many spurs or tees as you wanted. As long as there was a pair of wires going to each addressable device it would work! Obviously the cables would have to suitable electrically etc.
For BS 5839 part 1 2002 you would have to consider the effect that any wiring fault would have on the overall system. A single wiring fault shouldn't affect the protection in more than 2000m2 and two simulutaneous faults shouldn't affect the protection in more than 10,000m2.
Short-circuits are the biggest potential problem (as previously discussed) and the therefore short-circuit isolators should be used as necessary.
In the system you are talking about you could probably be able to install a two loop addressable panel and spur off all 12 existing zone wire cables from it via short-circuit isolators, change all the devices to addressable and you would then have an analogue addressable system without having to form the existing cables into a loop.
Obviously there are a whole number of BS5839 factors to take into account, which even for someone as 'wordy' as me, would take a long time to explain in writing. If you are seriously contemplating this option let me know and we'll make contact by phone and I'll advise you what to look out for.