I know it is all now supposed to be non-prescriptive, but regardless of that the guides are there to work from. The guides mention letting a few more people through an inward opening door dependant on risk.
"The number of 60 can be varied in proportion to the risk; for a lower risk there can be a
slight increase..."
150 is not a slight increase. Plus you have members of the public.. therefore you have vulnerable groups?
I guess at the end of the day it should be in the risk assessment, and someone has to take responsiblity for the decision. Should it go wrong then FA will look for reasons/shortcomings/bad decisions. If you know it cannot go wrong then there should be no problem.
Another way to look at it, if there was a problem could people get out quicker/safer through outward opening doors? If so RRO 14(2)(b) & 14(2)(d) surely help?
(2) The following requirements must be complied with in respect of premises
where necessary (whether due to the features of the premises, the activity carried on there, any hazard present or any other relevant circumstances) in order to safeguard the safety of relevant persons—
(b) in the event of danger, it must be possible for persons to evacuate the premises as quickly and as safely as possible;
(d) emergency doors must open in the direction of escape;
Also with regards high ceilings, lecture theatres tend to be raised towards the rear of the room so ceiling height is not too good for the people sat at the back, or anyone having to evacuate up the steps.