Well I am not going to argue that you can except limitless inward opening doors, just that I had not seen/heard the restriction of having one inward opening door restricting the exit capacity to 60,regardless of the numbers of other outward opening doors,I do not understand the reasoning behind that.The 'old' yellow guide for places of entertainment did limit a space with a single (outward) opening door to 50 in the smaller halls, and current ADB my understanding of '6.14' -'the door of any doorway or exit should,if reasonably practical,be hung to open in the direction of escape,and should always do so if the number of persons that might be expected to use the door at the time of the fire is more than 60' applies to the door,not the space.A room that had a single inward opening and another outward opening door would still be restricted to 60,because you would still discount the outward opening one for fire(and Iam sure there must be an argument whether that is logical!)-assuming floor space/td/distribution factors ok.But after that surely you must take into account any other exits.How could you have a large hall with a floor capacity of say 1000, 5 double outward opening doors of 300,one single inward opening door, and say they can only have a capacity of 60?I find it difficult to believe that is what you mean so something has been lost in translation!