Many assessments of this rate of flow have been made following tests, (particularly those using Paris firemen in 1938 and 1945 and the London underground).
The generally accepted rate is 40 persons per minute per unit exit width.
The width of a unit corresponded to the average shoulder width and was determined at 525mm. Two units of 525 (i.e. 1050mm) were required for 2 people to travel through, shoulder-to-shoulder.
However, due to overlapping effects, further units of width required were found to need only another 450mm. Hence, 3 units of 525 + 525 + 450 = l500 mm and 4 units of 525 + 525 + 450 + 450 = 1950mm.
Units greater than 4 units wide were considered to slow flow rates down, and so the maximum width of an exit is 4 units or 1950mm.
It should be noted here that the figure of 40 per minute was an average figure while the actual figures varied between 20 and 170.