My client is installing a new 2 stage alarm system in his 4 floor building. There will be close on 800 persons in the building. He has asked me how long can people remain at their desks when the alarm is sounding intermittent i.e standby, before the system switches to full evacuate tone? This is to enable an orderly evacuation and to prevent congestion on the stairs. Am I correct in saying if the fire was on the 4th floor, for example, that floor and the one below would immediately go into full evacuation mode and the remaining floors would go on standby? If it was the 1st floor, would the ground and 2nd floor go on full evacuation and the others on standby? The escape stairs are all 1 hour rated.
Quuick reply-may not be 100%:
a)max recommended time 6 minutes
b)no, just the 4th floor (phased evac-fire floor and one above plus disabled persons on all floors
c) just the first and second.
d)also stairs need to have lobby's/protected corridoor approach for phased evacuation, each floor needs to be a compartment floor(there is a fair chance in that size builsing they may not be.You will also need to calculate your stair capacity,although unless numbers are increasing,they may be okay as existing