As I know that Wee B is a very busy man I thought I’d add my two-penneth, as, in a previous life, I had something to do with the ‘new’ concept.
The AOV at the top of the stair only acts as an inlet when smoke from the lobby/corridor is ventilated to a smoke-shaft which is sealed at the base (either naturally or mechanically driven). This is due to the stack-effect (or pressure drop due to a mechanical fan) in the smoke shaft causing the lobby/corridor to be under reduced pressure. This will cause air to be drawn from the stair to the lobby, provided there is some form of inlet in the stair. There will be a flow from the stair to the lobby when the stair door is open, preventing smoke from entering the stair at all using the concept of depressurisation….and when the stair door is closed, there will still be a sufficient pressure difference across the stair door preventing smoke from entering the stair via any possible gaps around the door.
The bottom line is;
door to stair open = stairway clear of smoke
door to stair closed = stairway clear of smoke
Of course, if another source of inlet air is provided to the stair…say the Fire Service prop open the door at the base of the stair (which leads to external air), then the inlet air may well come from there instead, and the AOV at the top may be ‘neutral’, it is dependent on the location of the fire. The inlet air will just take the path of least resistance. The AOV at the top of the stair provides inlet air (similar to a U-tube shaft) prior to the stair being accessed by the Fire Service/or occupants so that the system works from detection.
This concept worked for ‘cool’ smoke as well as ‘hot’ smoke, as the magnitude of stack effect required (for naturally ventilated shafts) was much less to prevent smoke ingress to the stair for ‘cool’ smoke. Of course, mechanically ventilated shafts will deal with most temperatures of smoke (in line with the temp rating of the fan), provided that door opening forces are not exceeded.
The main aim of this approach is to keep the stair clear of smoke. Conditions in the lobby/corridor are generally untenable when the door to the fire room is open (when the stair door is either open or closed), and conditions are not always much better for smaller quantities of cooler smoke. Because of this, the ‘new’ approach focussed on protecting the stairwell.
If you want to provide protection to the lobby/corridor as well, you really need to provide some form of dedicated smoke control system for that area (this is where high level vents and low level inlets are required).
When smoke is ventilated from the lobby/corridor via an external window, the pressure difference between the lobby/corridor and the stair is not large enough to prevent smoke from passing into the stair when the door to the stair is open (there is no stack effect). So the vent at the top of the stair WILL act as an outlet in this case.
Well……that’s probably as clear as mud….but I did try.