My interpretation of Volume 2 of Document B is that fire alarm systems are not a requirement in the communal areas of purpose built flats, only the individual dwellings. However, I note that most of them appear to have them. Although it is without doubt good practice to install a system, it doesn't seem likely to me that a developer will install a system unless he has to, so why are they doing it? Is it due to the local BCO allowing some deviation from the strict requirements of ADB on condition that an AFD is installed to compensate. If so, does anyone know if there is guidance on this subject from Building Control. Alternatively, I may have completely misunderstood the requirements. In this case can someone enlighten me.
As you correctly state ADB does not look for AFD to communal areas, although we are getting examples under the RRO where certain groups are requesting AFD to the communal areas as a recommendation under the Fire Risk Assessment to minimise the risks for people who could be working in the communal areas, and it may be that this is now being considered and implemented at design stage.
As Kurnal says, AFD can be used to compensate for deviations from standard guidance or to address a particular design issue, and these have to be assessed on a case by case basis in both new build or conversion works. It is important however to consider HOW the alarm will activate. As Kurnal says the assumption in apartments is, that the occupants of apartments other than the "fire apartment" to stay put in relative safety due to the high levels of compartmentation.
In taller apartments with single stairs, a simultaneous alarm activation in the communal areas could result in people evacuating their apartments and heading down the stairs when the building has been designed for them to stay put, and this could have implications on the fire service access.
I think this may be a reaction to what we are seeing since the introduction of the RRO.