Thanks Graeme
Found some xenon beacons on the net at 70ma EACH!!!
Thats what raised the initial question!
where would I have got the sounder control units from? Sorry again but I have not had this before.
How would these link to a conventional panel and still monitor the cabling?
If you want to change sounders for combined sounder beacons then as already stated work out what the extra load will be, then do a battery calc to make sure the standby isn't going to be affected.
Also check the fuse rating of each circuit, the 800mA could be a total alarm load, but the circuits might be rated at 500mA + each.
Re the "C-Tec 4 way splitter", if your adding sounder circuits then you trigger this from one of your panel sounder circuits....you need a 24volt supply to be feed the splitter and need to be careful where you pick this up from your panel, or you can install a separate PSU for the splitter. Any fault on any sounder circuit is then indicated through the trigger circuit from the control panel.
Or you can go somewhere like Kentec and get a splitter in a box with PSU built in.