1. It doesn't matter what the guides said in those days, if there were any. What matters is that the building is safe for those entering it today. Research has certainly moved on since the sixties.
2. Having said that I think I have some of the original smoke control documents at work. They're from the early 60s - I'll get back to you when I've rooted them out. I don't refer to them often!
3. It's not in S****horpe, is it?
4. If it's small enough, it might fall within the spirit of the appendix, A I think, to part 10. Basically, if it is smaller than the upper limit for an uncompartmented shop then it can be treated as such (i.e. no sprinklers, no smoke control). Worth a look.
4. If all units have secondary exits, you might think, on the face of it, that the mall could be sacrificed - that is to say, accept that it will fill with smoke and be lost for means of escape because everyone can leave by the alternatives at the rear of the shops they're in.
But it's not quite that simple for a number of reasons. For example:
people will be affiliated with other people in other shops and will want to meet them before evacuating,
the mall itself will have it's own population of shoppers who will need satisfactory moe,
the rear exits are probably only designed to cater for the occupants of a single shop unit,
fire will probably be able to travel from the unit of origin to other units and possibly the whole mall,
fire fighters will have difficult access,
etc.
5. The mall smoke control will almost certainly not work if there is a fire in a shop. Smoke control systems can only cope with fires that are limited to a certain design size. They cannot cope with fully involved fires. This has always been the case.
6. You may be presented with some reasoning why the fire will be restricted to some size. Don't believe it without the most rigorous of justifications.
7. Nothing much has changed in 40 years. We're still getting crap proposals.
In the 60s, though, you could excuse their ignorance because the style of building and the science underpinning it was new.
Nowadays, the science is still fairly new but designers have an over-confidence in the capabilities of fire engineering partly induced by the fact that few fire engineered building have burnt down yet.
They will, given time.
8. This area is my speciality - if you want to email me details I will be able to help.
Stu