Author Topic: High-Rise  (Read 13023 times)

Offline jasper

  • Sr. Member
  • ****
  • Posts: 294
High-Rise
« on: December 14, 2007, 12:04:01 PM »
Could anyone point me in the right direction for some research I am doing on fire safety and risk assessment in multi-storey blocks of flats (apart from the obvious ABD)

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
High-Rise
« Reply #1 on: December 14, 2007, 01:44:29 PM »
Narrow it down a bit.

Offline jasper

  • Sr. Member
  • ****
  • Posts: 294
High-Rise
« Reply #2 on: December 14, 2007, 03:17:17 PM »
current standards and trains of thought, as in lessons learned from high-rise fire throughout the world
also I cannot understand how no detection (even heat) to the common areas is required

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
High-Rise
« Reply #3 on: December 14, 2007, 03:25:31 PM »
In the UK its a defend in place strategy, so theres not much point having a common alarm.

Theres the BRE report on smoke control http://www.bre.co.uk/adb/page.jsp?id=555

And I think the findings of the incident in Herts where two firefighters is now on the Herts website.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
High-Rise
« Reply #4 on: December 14, 2007, 10:00:55 PM »
BS5588 part 1 gives more information and commentary than ADB. For the history of fire safety design of  flats it would also be useful to look into the former guidance CP3 Chapter 4 part 1 1971.

Offline slubberdegullion

  • Full Member
  • ***
  • Posts: 136
High-Rise
« Reply #5 on: December 18, 2007, 02:05:14 AM »
Quote from: jasper
Could anyone point me in the right direction for some research I am doing on fire safety and risk assessment in multi-storey blocks of flats (apart from the obvious ABD)
One of the main areas of interest in these buildings is the ventilation of common escape routes.  This can be very relevant to the fire risk assessment.  There's been recent work on this - suggest you google "ventilation flats" or similar, but look out for the BRE research.  Also, I think Howard Morgan published something a year or two ago in the IFE magazine - can't recall the details - check the mags.  Fire engineering firms have tried to be quite inventive in the last few years when designing ventilation systems in such areas.  They haven't always proved sufficiently effective.

Stu

Offline slubberdegullion

  • Full Member
  • ***
  • Posts: 136
High-Rise
« Reply #6 on: December 18, 2007, 11:15:38 PM »
Here's a tale. Consider it anonymous.  Consider that it didn't happen last night in a block of flats just like 10,000 others throughout the country.

Low rise block of flats.  
Three flats per floor.  
Common escape corridor leading to single staircase.  
Corridor ventilated by permanent grill at one end, no ventilation at the other end (staircase end).
Fire in a flat on an upper storey.  
Occupant runs out flat.  
No self closer on front door and door left open.  
Occupant knocks on doors of neighbours in his corridor to alert them to fire.  
Dead end corridor.  
(Front doors are fire doors, though as stated, no closers.  
Windows (not fr) between flats and corridors.)
Heavy smoke logging of corridor due to fire flat door being left open.
No subsequent evidence of smoke penetration into neighbouring flats.
Neighbours probably would have been perfectly safe if they had stayed in their flats watching the telly.
Neighbours, because they knew of fire, wanted to leave the building but were unable to because of smoke logged corridor.
Attending fire service confronted with neighbours shouting for rescue from their flat balconies.
Neighbours 'rescued' by fire service by ladders.
Fire contained to flat but evidence of heavy smoke logging in corridor.
Quite clear that corridor was impassable during fire.

I'm not going to suggest an end to the 'defend in place' fire strategy but I have concerns about it and about ventilation of common corridors.  Anything you can add, Phil?

Jasper, I think this is an important area for research.

Anyone else any thoughts about how to improve these buildings?

Stu

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
High-Rise
« Reply #7 on: December 19, 2007, 08:56:10 AM »
How about giving instructions to the tenants in what to do incase of fire.  It is not the building design or the building fault it is how we use them.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
High-Rise
« Reply #8 on: December 19, 2007, 05:25:10 PM »
Stu
Your posting reminds me of of the early 1980s when the then current hotels guide did not recommend self closers on bedroom doors where there was two way travel. Everybody closes their hotel room door dont they.
Then one night a staff member had a fire in his room and in the panic evacuated leaving the bedroom door open and I think this led to a death. The guidance was then changed so all bedroom doors were self closing.

BS5588 part 1 has always recommended fire safety advice to be given to tenants trouble is nobody bothers to issue it and nobody reads it, remembers it or brings it to the attention of tenants.

In any case in the situation you describe a stay put policy would not be tenable with plain glazing between flats and corridors. (Just like in many 1960s blocks)

The answer- upgrade the glazing, provide self closers and educate the tenants. It may just work a bit.

Offline PhilB

  • Hero Member
  • *****
  • Posts: 963
High-Rise
« Reply #9 on: December 19, 2007, 06:31:02 PM »
The problem with the example you refer to Stu was two-fold.
1) There was no self-closer on the front door,
2)FR glazing between flats and common parts has been replaced with nice double glazed units.

The person who risk assessed the common parts, if it has indeed been assessed, cleary has not identified these problems.

That failure to identify and rectify the problems placed relevant persons at serious risk.......consideration should be given to a prosecution but I won't even go there!!

It was an interesting job, several rescues by ladder.

How many identical problems exist throught the UK I wonder?

The answer as Kurnal points out is to replace glazing and fit self-closers......perhaps try and educate the occupants but are they likely to stay put when they can see smoke and flames?

Offline jasper

  • Sr. Member
  • ****
  • Posts: 294
High-Rise
« Reply #10 on: December 19, 2007, 07:01:05 PM »
this is becoming an interesting topic (for me)

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
High-Rise
« Reply #11 on: December 19, 2007, 09:28:44 PM »
Didn't Alan Wroclawski and Pat Carey write a tome on High Rise buildings in the late 80's?  I have a copy of what I think they did somewhere, mind you I might be going mad and be refering to something completely different.  As regards self closers, as soon as the individuals locks themselves out once they will come off and the problem will not go away.  Education is a better method but how you go about that is difficult.

The problem is at work, get out and stay out, very few people die, at home stay in and people die.  We in the fire industry send mixed messages and expect that everyone understand different strategies.  After 9/11 those in the tower in canary Wharf wanted out as soon as an alarm sounded, not good in a phased evacuation building.  Now after numerous drills and test they don't want to move.

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
High-Rise
« Reply #12 on: December 19, 2007, 09:39:10 PM »
Picking up on Joker's comment we have done a lot of FRA's in these types of premises from new builds, conversions and very old properties.  The common findings we have found are the replacement of the flat doors with UPVC ones, or the glazing in the door has been replaced with non FR type.  We have included guidance from BS 5588 Part 12 in each of the FRA's which we suggest that the management companies communicate to all residents where possible.  See below for info.

Any emergency plan should be communicated to all relevant persons where possible.  
                                         
Example of a fire instruction notice for use in flats.
(based on that suggested in British Standard 5588-12: 2004)

This building has been built in such a way as to protect the people in it if a fire breaks out.
The important thing to remember is that if the fire starts in your home, it is up to you to make sure that you can get out of it.
AT ALL TIMES
o   Make sure that the smoke alarms in your flat are tested.
o   Do not store anything in your hall or corridor, especially anything that will burn easily.
o   Use the fixed heating system fitted in your home. If this is not possible, only use a convector heater in your hall or corridor. Do not use any form of radiant heater there, especially one with either a flame (gas or paraffin) or a radiant element (electric bar fire).

IF A FIRE BREAKS OUT IN YOUR FLAT
               -  If you are in the room where the fire is, leave straight away,    
                   together with anybody else , then close the door.

o   Do not stay behind to try to put the fire out, unless you have received suitable training.

o   Tell everybody else in your flat about the fire and get everybody to leave. Close the front door and leave the building.
o   Do not use the lift.
o   CALL THE FIRE SERVICE.
IF YOU SEE OR HEAR OF A FIRE IN ANOTHER PART OF THE BUILDING.
o   It will usually be safe for you to stay in your own home.
o   You must leave your home if smoke or heat affects it. Close all doors and windows.

CALLING THE FIRE SERVICE.
              -  The Fire Service should always be called to a fire, even if it only seems
                to be  a small fire. This should be done straight away.
              -  The way to call the fire service is by telephone as follows.
                 1) Dial 999.
                 2) When the operator answers, give the telephone number you are
                      ringing from and ask for FIRE.                    
                 3) When the fire service replies tell them clearly the address where the
                      fire is. APARTMENT NUMBER?
                      ADDRESS
                 4) Do not hang up until the fire service have repeated the
                    address to you and you are sure they have got it right. The fire service
                     cannot help if they do not have the address.

Offline saddlers

  • Jr. Member
  • **
  • Posts: 61
High-Rise
« Reply #13 on: December 19, 2007, 10:39:56 PM »
Don't forget that a majority of these blocks are also only served by a single stair. Simultaneous evacuation is not a good idea in this scenario for a multitude of reasons (fire service access, stair widths etc.) DCLG at a recent seminar still stated that the "stay put" method was very successful on the whole, and there were no imminent plans to change it.

It would be interesting to know how many incidents had occurred where residents other than those in the flat of fire origin were affected.

I have to admit if I was in a flat on the 10th floor and I saw smoke rising externally from a much lower floor, I would be very tempted to evacuate!!

Detection in the common areas would only be beneficial to the people in those areas (cleaners, caretakers etc) hence the recent issues that have arisen under the RRO. The issues that would arise from a communal alarm system would be massive, the potential for false alarms, neighbours to annoy each other etc etc, maintenance issues etc.

If we decide to only provide sounders in the communal areas what good would they be when you are asleep, and in many cases would have two fire doors and an acoustic separating wall between you and the sounder.

I believe the current system works quite well combined with the levels of compartmentation, and admittedly is not perfect, but I just cannot see how any other solution would be perfect either.

Historic buidlings or those that have been unofficially tampered with, will always have issues, but a compliant scheme should in general provide a decent level of fire safety.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
High-Rise
« Reply #14 on: December 20, 2007, 10:53:11 AM »
well said - it works - leave it alone