Im involved with a number of works to a 20 year old Civic Centre building. Its a four storey building which houses around 800 staff, but has a large central full-height atria. The curtain walling between the internal offices and the atria is not FR and from what I understand, the deluge system was installed as an engineered solution to this. The system is configured with a 125mm wet rising main which feeds eight 'zones' of pipework with open heads positioned every couple of metres in the atrium over the glazing line. The water is held back by a 24v solonoid between the main and the first sprinkler head in each zone.
Thats the easy bit...
Within the offices there are 10 'zones' of of 1/2" pipework fitted with standard sealed sprinkler heads which, again follow the glazing line. Each zone is fitted with a non-return valve and a pressure switch, upstream of the valve/switch the zones are connected to a main and in-turn a compressor. Activation of one of the zones, causes the pressure to drop, closing a relay in the panel. A fire signal is required from the FAP to close a second relay and open the solonoid valve to the coresponding deluge 'zone'.
Theres very little info on the system, the installers only have as fitted drawings, what I`d like to know is:
Is there a standard for such installations (Curent service provider seems to think not)?
Does the system need to have a mechanical detection, or could the pneumatics be replaced with smoke / heat detectors on the existing addressible FA mounted on both sides of the glazing configured for double / tripple knock ?
Are such systems still installed ?
Paul