This may be of some help
Extract from the Irish Building Regs 2006 TGD B
Where people can go onto the storage tiers in the course of their normal use, reduced levels of fire
resistance in the construction of the raised storage platforms (or even little fire resistance so as to
permit an unprotected steel structure) may also be acceptable provided the following conditions are
satisfied:
(a) the structure has only one tier and is used for storage purposes or access to plant or machinery only;
(b) the number of persons likely to be on the floor at any one time is low and does not include members of the public;
(c) the layout is such that any persons on the floor would be readily aware of any fire starting at the lower level; and
(d) at least one stairway serving the raised floors,platform or tier discharges within 3 m of an exit from the
building.
Features of layout or design that would allow occupants to be aware of a fire starting at the lower level include the use of perforations in the floor of the structure, or leaving a space between the edge of the platform and the walls of the room housing it, to make the smoke and the sounds of the fire obvious.
If the floor is more than 10 m in width or length, an automatic fire detection and alarm system should be
used to provide sufficiently early warning.