Hi Kurnal
I work closely with 2 fire alarm companies that deal with all fire alarm and emergency lighting issues resulting from the fire risk assessments that we have conducted, one operates in the North West and the other UK wide. Predominantly both companies advocate that the 2 visits per year in accordance with the BS is fine (unless, age faults etc as mentioned above is an issue) However I have come across a lot of other alarm companies (I have to say large national ones) that seem to push the 4 visits per year regardless.
In my opinion a risk assessment shouldn’t only advise on meeting the legal requirements of the FSO and current fire safety guidance but also offer cost effective solutions to a range of fire safety issues. I have a particular bee in my bonnet on this one as I see many situations where the alarm company cherry picks from BS 5839 and often designs a fire alarm system that goes over and above what the client requires or has asked for. Lets remember that BS 5839 states “ The need for a fire alarm system in any specific building will normally be determined by the authority responsible for enforcing fire safety legislation in that building and/or by a fire risk assessment carried out by the owner, landlord, occupier(s) or employer(s), as appropriate”( Commentary 4.1) In my view the FRA should be the starting point when designing the system when often it is never taken into consideration during the fire alarm design stage but produced afterwards sometimes highlighting deficiencies, much to the clients confusion and frustration.
Over the past 2 years I have developed a system where when the FRA has been conducted and identified fire alarm deficiencies we work with the fire alarm company to provide a cost effective solution for the client. The FRA’s differentiate between what category alarm system is required for life safety only or for additional property protection. The tendency at the beginning was the alarm company would throw L1 at everything and were very reluctant to design and commission L5 systems to meet a specific fire a safety objective, until the benefits were explained.
I realise I am going on a bit now but in short to your question I feel that SOME companies do try it on with the 4 visits when the 2 will do. If you need any more info I can provide you with a contact at one of the alarm companies and you can discuss further if you feel that would be of help.