I would also remind you that not too long ago it was a condition of being issued a fire certificate that equipment was kitemarked. I seem to remember that this condition was dropped 6 or 7 years ago? I do not have sufficient interest in your rantings to look it up!
No it never was, the Fire Service could not specify this, they could recommend. What they could do was require extinguisher provision, that the equipment was kitemarked could not be required.
If a client had no duty to the people dependant on him for their safety, anarchy would rule.
We as a company have a duty to the client to provide equipment that is fit for purpose, if this is not accomplished by using equipment that is approved by a third party, then what do you suggest?
You have a duty to the client to provide fit for purpose equipment, as per the Sale of Goods Act, the client must provide safety equipment fit for purpose under HASAW, but they do not need to have kitemarked, fre rated, or third party accredited equipment. Nor should you be so conceited as to refuse to service any equipment, unless it does not comply with legal requirements. You must not impose your own dubious standards on customers, by all means try and persuade them to part with money for your [no doubt] expensive replacements of their equipment, but refusing to service them because they have no marked fire rating or kitemark is not professional.
Also all too often we are asked to service refurb CO2 extinguishers that have not been fitted with new valves.
We also come across "rag and tag" merchants who do our industry no favours at all, going by your comments above, i would guess that you are also in favour of these cowboys?
I am in no way supporting cowboy operators. Any refurbished CO2 must be fitted with a new, or fully refurbished, valve, that is part of the process. However it is not required to be new, the reason new ones are generally fitted is that BS5430 testing means that the work to fully refurbish a valve compared to the cheap replcement cost makes it uneconomical not to use new ones.
DaveyH Chris is entirely correct, that there is no legal requirement to comply with any BS recommendation and that the risk assessment would be all the court would require. All too often "legal requirement" is used by disreputable compnaies to sell BS requirements to customers. Let's hope some are savvy enough to see through that.