detection in a swimming pool
« on: February 01, 2008, 10:41:33 AM »
Currently looking at a sports facility with swimming pool. The alarm system as specified is an L2; however it is not proposed to install detection in the pool area. The pool area has large spectator area at one side. The L2 system has been specified as a compensatory feature for some inner room situations and some areas where the open spatial planning rules are not fully complied with.
2 questions,

1) is it normal ‘not’ to install detectors in a pool environment, even with a spectator area
2) If detection is provided, which type would be suitable for this environment?  
Your expert answers would be greatly appreciated.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
detection in a swimming pool
« Reply #1 on: February 01, 2008, 10:54:58 AM »
Difficult question- the pool is a very hostile environment and access for maintenance to point detectors would be a nightmare. The risk is very low generally and the spectator area may be a red herring- why would we need detectors in this area whilst persons are present- because people are the best form of detection.
Further review the fire risk in the pool, look at waste bins and substitute smaller, non combustibles, separate off any plant rooms.  Having done this there will be no point in putting detection in there other than perhaps heat for property protection out of hours.

I wonder if L5 would have been more appropriate compensatory feature? if the pool is the access room then the risk is probably so low as to allow a relaxation of the inner room rules. After all is the fire risk in a swimming pool any higher than in a  protected corridor or staircase?

Offline John Webb

  • Hero Member
  • *****
  • Posts: 838
detection in a swimming pool
« Reply #2 on: February 01, 2008, 11:06:53 AM »
There may be a greater need to consider the installation of detectors if the pool is covered over for part of the year for other sports or functions.
If the Risk Assessment concludes that detection is needed, then beam detection would be the best bet. These can be sited on end walls of the building for easier installation and subsequent access but still cover the whole floor area. An aspirating system might also be suitable, but you'd have to consult the makers about their suitability in, as kurnal says, a hostile environment.
John Webb
Consultant on Fire Safety, Diocese of St Albans
(Views expressed are my own)

Offline BHCC

  • Newbie
  • *
  • Posts: 30
detection in a swimming pool
« Reply #3 on: February 01, 2008, 12:01:52 PM »
I would think about beam detection in the pool area

Offline BCO

  • Jr. Member
  • **
  • Posts: 56
detection in a swimming pool
« Reply #4 on: February 01, 2008, 12:16:53 PM »
beam detection is out, due to water polo!

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
detection in a swimming pool
« Reply #5 on: February 01, 2008, 12:48:13 PM »
Beam detection can be set up with a range of parameters- including percentage obscuration and duration of obscuration- birds in warehouses can otherwise be a problem!

Offline Thebeardedyorkshireman

  • Jr. Member
  • **
  • Posts: 96
detection in a swimming pool
« Reply #6 on: February 01, 2008, 01:16:12 PM »
The main problem will be corrosion of metal parts due to chlorine in the atmosphere. You should specify marine grade detectors if you install point type. You may be able to get a special enclosure for the beam TX / RX with the control equipment in a safer area. Try double knock for the beams if you think polo may be an issue, but I think you will have problems with beam adjustment due to impact from the ball.
 Aspirating may be the way to go but you will need confirmation from the manufacturers about the atmosphere inside the sensing chamber and long term reliability.
Dave

Offline Dinnertime Dave

  • Hero Member
  • *****
  • Posts: 819
detection in a swimming pool
« Reply #7 on: February 01, 2008, 01:39:44 PM »
I am at present dealing with a similar sounding building. As its a Local Authority building we were involved at the design stage. L2 system was specified in all areas except the pool for the reasons discussed. we avoided inner rooms in the pool area which are prodominantly plant rooms anyway, which by their nature required outside access.

My only real observation is this - Is the means of escape really that reliant on detection within the pool area? if so why?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
detection in a swimming pool
« Reply #8 on: February 01, 2008, 02:47:22 PM »
Quote from: Dinnertime Dave
I am at present dealing with a similar sounding building. As its a Local Authority building we were involved at the design stage. L2 system was specified in all areas except the pool for the reasons discussed. we avoided inner rooms in the pool area which are prodominantly plant rooms anyway, which by their nature required outside access.

My only real observation is this - Is the means of escape really that reliant on detection within the pool area? if so why?
What are the inner rooms used for?
We're not Brazil we're Northern Ireland.

Offline BCO

  • Jr. Member
  • **
  • Posts: 56
detection in a swimming pool
« Reply #9 on: February 01, 2008, 03:32:30 PM »
In the pool there is a first aid room and a pool store which are inner rooms to the pool. The pool inner rooms could easily have vision panels (instead of detection in the pool).
Generally throughout the building there are many inner rooms as there is a large café area which is open to many circulation areas and escape routes with voids that breach floors, this is generally the reason why an L2 has been specified.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2484
    • http://www.firewizard.co.uk
detection in a swimming pool
« Reply #10 on: February 01, 2008, 11:20:46 PM »
Surely an L2 with bits excluded (that normally would be included) isn't L2 at all but a L5 risk based system?

Just because a system is L5 doesn't mean it is only a couple of heads, it could be dozens, but located (& excluded) to deal with a specific issue - in this case access rooms to inner rooms & areas deviating from normal construction codes.

Does the pool have any areas of fire risk that could not be readily and promptly detected by the occupants? If so then detection of an appropriate type should be considered, but for the area around the pool itself surely the occupants would detect a fire first before a head could and that in an area that is largely wet and tiled the fire risk was less and hence why they decided manual call points alone would suffice?

Just trying to see where the original specifiers were coming from
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline slubberdegullion

  • Full Member
  • ***
  • Posts: 136
detection in a swimming pool
« Reply #11 on: February 01, 2008, 11:32:04 PM »
I once dealt with a pool in a sprinklered building and I had no qualms about agreeing to omit the sprinklers from the pool area (no spectator area or anything like that around it).  If there's no real need for something, there's no need to install it.

Stu

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
detection in a swimming pool
« Reply #12 on: February 02, 2008, 08:04:50 AM »
Quote from: BCO
In the pool there is a first aid room and a pool store which are inner rooms to the pool. The pool inner rooms could easily have vision panels (instead of detection in the pool).
Generally throughout the building there are many inner rooms as there is a large café area which is open to many circulation areas and escape routes with voids that breach floors, this is generally the reason why an L2 has been specified.
Wouldn't concern myself very much about rooms where nobody is employed and where access is only for a very short period eg store.
A room where privacy is required, eg first aid room, could be provided with one way glazing.
We're not Brazil we're Northern Ireland.

Offline davio1960

  • Newbie
  • *
  • Posts: 37
detection in a swimming pool
« Reply #13 on: February 08, 2008, 09:38:23 PM »
Try researching city of Winchester swimmimg pool fire late 80's early 90's.
Strangely swimming pools "go like a train"
Davio1960
Regards Davio1960

Offline g4vjc

  • Newbie
  • *
  • Posts: 8
detection in a swimming pool
« Reply #14 on: March 11, 2008, 11:00:38 AM »
I have a similar situation regarding a leisure centre with a swimming pool (with spectator area) for which I'm doing the design for an electrical contractor.

The response I've got from him with regard to the category of system is as is often the case "better make it an L1". On this occasion it's making it difficult as detection in the pool area will be a nightmare, point detectors difficult due to future access which leaves beam detection as the only real option.

Would it be reasonable to detail the omission of automatic detection within the pool as a variation due to the minimal fire risk, high possiblity of false alarms due to condensing moisture and future access for maintenance issues. The beam detectors my company tends to use also only have an IP rating of 42 so this is also an issue.

If it were an L2 I'd be confident in omitting it but not sure on an L1, anyone had any similar experiences?