Author Topic: Voice Alarms  (Read 4164 times)

Offline jasper

  • Sr. Member
  • ****
  • Posts: 294
Voice Alarms
« on: February 18, 2008, 11:45:49 AM »
I am trying to find out the requirement for voice alarms in public buildings, I know that this was in the old yellow guide but this has been revoked, have also looked in the rro guide and no mention. I am looking at a covered market area and whether it should be fitted

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Voice Alarms
« Reply #1 on: February 18, 2008, 12:31:48 PM »
Surely, in these types of premises you would want a staff alert system not a "sounding alarm".  Most people are visitors and would not know where the escape routes are or where they lead to.  Therefore a silent staff alarm would be more suitable and the staff can then lead visitors away.  BS 5588 part 6 is for assembly premises and there is only mention of the above in  there.

Offline jasper

  • Sr. Member
  • ****
  • Posts: 294
Voice Alarms
« Reply #2 on: February 18, 2008, 04:43:35 PM »
it is a 1600m2 market, single storey btw

Offline FORRIE

  • Newbie
  • *
  • Posts: 18
Voice Alarms
« Reply #3 on: February 18, 2008, 10:02:43 PM »
JASPER
BS 5839 Part 8 -1998 Code of practice for the design,installation,commissioning and maintenance of voice alarm systemd may be of some help to you.