'You do need to be carful where people are proposing "design freedoms" or trade offs on the back of the sprinklers being installed. I would suggest that in such cases the specification of the sprinklers may need to be higher than BS 9251 provides'.
How much higher? This is where it becomes subjective and there is no clear guidance available.
Any "design freedoms" must be decided upon after full analysis of the effects of the compensating feature and of the effects of omitting whatever is being omitted. It's a balancing act and cannot be entered into lightly.
For example, there have been cases where recessed sprinkler heads have breached compartmentation in buildings. That is, the sprinkler system will operate for 10 or 30 minutes, but after that time it leaves a hole in what would otherwise be a line of fire resistance (the plasterboard ceiling). If the required level of fire resistance in the building is longer than 30 minutes (or 10 minutes!) then there is the potential for a breach. This is hardly what the designers anticipated and it illustrates how rigorous analysis is required.
It's also fair to say that things get a bit hairy in very tall buildings when they are on fire
The residential standard has to be the one for flats. The ten minute domestic standard is for houses where everyone is likely to be out in ten minutes (if they're going to get out). Flats are different. If you are comparing an individual flat to an individual house, then yes the same principle applies, everyone, if they are going to get out, should be out in ten minutes. But there is the added complication of the rest of the building. Ok, if the compartmentation is up to scratch then there should be no reason why anyone else should even find out about the fire, let alone evacuate, but maybe the compartmentation isn't always as good as we'd like to think it is. To come up with a particular solution for a particular building we're back to the balancing act.
perhaps the BS could be tidied up a bit to deal with this
There are many areas where the BS does not give complete answers, but application of sound reasoning when interpreting the principles being strived for should provide best solutions.
But ADB also states that ‘Sprinklers only need be provided in individual flats’.
Therefore corridors and common areas are unsprinklered.
What is the point of sprinklering an area where there will never be any fire load?
1. Flowswitches and audible alarms
For resi it states that... 'alarm arrangements should be in accordance with the authority having jurisdiction'
We should discuss and agree with the relevant authorities applicable to the project
The fire service may find it useful to have an indication outside a flat that the sprinklers are going off inside, but maybe it would be undesirable to raise the alarm for other residents. Maybe it would be desirable. It depends. So that's where the AHJ can have their say and tie the sprinkler arrangements in with the more general fire strategy for the building.
Stu