AFD Panels
« on: March 13, 2008, 02:54:41 PM »
There are 4 seperate blocks of flats each containing 5 flats that are joined like terrace houses with one basement car park running below all 4. There are 4 seperate front doors, one to each block, would there need to be a seperate ( independant ) AFD panel in each block or only in one, connected to the others via repeater panels?

Offline john01

  • Newbie
  • *
  • Posts: 3
AFD Panels
« Reply #1 on: March 17, 2008, 09:21:17 AM »
Test

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
AFD Panels
« Reply #2 on: March 17, 2008, 09:25:55 AM »
It all depends on the fire compartmentation between the flats and the car park.
Do  the stairs from any of the blocks of flats go down into the car park?

Midland Retty

  • Guest
AFD Panels
« Reply #3 on: March 17, 2008, 02:46:52 PM »
If you have a minimum seperation of 60 minutes fire resistance between each block seperate AFD wouldnt be required.

EVen without that level of seperation, I still wouldnt recommend interlinking them.

Just ensure 60 min seperation between the flats and the car park. YOu would need AFD down there too. Might be worth linking the AFD from basement to all of the blocks as all residents should be given warningof a fire down there.