I have read conflicting info as to whether it should be checked monthly, 6 monthly and 3 yearly , and other info saying the 6 monthly test is now not needed , which is correct ?
Also can anyone be nominated as the responsible person to do the 3 yearly tests? or do they need specific qualifications ?
Emergency Lighting Testing & Maintenance
You must ensure that regular checks and periodic servicing and maintenance is carried out whatever the size of the premises and any defects put right as quickly as possible.
You, or a competent person nominated by you, can carry out certain checks and routine maintenance work. A competent person is someone who has the necessary training or experience, access to the requisite tools, equipment and information, and is capable of carrying out a defined task.
Maintenance may need to be carried out by a competent service engineer.
Where contractors are used, third party certification is one method where a reasonable assurance of quality of work and competence can be achieved.
It is recommended that checks and tests are carried out as follows.
Daily Check
All safety lighting units will have a visual indicator, usually a small red lamp, which, when functioning normally, will be illuminated. This indicates that the unit battery is receiving a constant electrical charge from the mains. This indicator lamp should be checked daily for operation. This simple check can be undertaken by staff who routinely work in a particular area for units in that area.
Any defects should be reported immediately for remedial attention.
Monthly Check
Switch on in the emergency mode by operating the unit’s test facility. If an integrated test facility is not provided then the sub circuit (not the mains supply) for that particular area should be interrupted for a period sufficient for all units to be checked that they are present, clean and functioning correctly.
At the end of the test the supply should be restored and a final check of each unit to ensure that the mains supply indicator lamp is operating normally.
The date and results of the test should be recorded and any defects reported for immediate remedial attention.
Six Monthly Check
Each unit should be tested as for the monthly check except that the period should be 1 hour for a 3 hour unit and 15 minutes for a 1 hour unit.
The date and results of the test should be recorded and any defects reported for immediate remedial attention.
Annual Check
Each unit should be tested as for the monthly check except that the period should be as per the full battery duration of the unit. This can be between 1 and 3 hours.
The date and results of the test should be recorded and any defects reported for immediate remedial attention.