when i sat the IFE advanced commisisoning course the tutor told us that it is up to the commissioning engineer to check the entire installation. Even opening up joint boxes and inspection terminations in detectors etc.
So how can Graeme compete by commissioning to IFE requirements, when others just follow the letter of BS and would have a customer who was more than happy with that (in fact, that is all
they want!)
......Surely if the designer and installer sign off their part as complaint then there should be no need to double check it.......
This is generally how BS thinks it should be. It assumes that the designer has his design right. It assumes that the installer has his installation right. These two 'certificate' their own parts as being 'spot on' and should take responsibility for what they have done.
However then BS goes and spoils it all by asking the commissioning engineer to do a certain amount of double-checking of the others and includes this in a section containing the requirement to check compliance of about 50 different recommendations within one clause on the model certificate!
Most importantly the designer and installer don't realise he has to do this because the 'model' certificate doesn't make this crystal clear unless you understand that is what is included in the phrase 'in accordance with recommendations of 39.2c.
This is why designers and installers hate a good commissioning engineer!
still...i have yet to see a design and install certificate from any job other then the ones i have been invloved from design to hand over.
How many times have I asked an installer at commissioning to confirm the category of the system and he says he doesn't know. I ask him what category is listed in the specification and he says it doesn't indicate any category. But BS doesn't recommend that the installer and commissioner have sight of any certificate before commencing commissioning. It doesn't even confirm what category he should check the system complies with!
It is quite obvious to me that 'commissioning' needs to be broken up into two parts.
The first part is to ensure the installed equipment functions correctly and could even be carried out in stages. It may be completed before the painters have finished and the floors are laid ( as the builder wants) The certificate for this should include a precise list of the type and location of every bit of equipment that has undergone this 'testing' commissioning. This commissioning could also include reports of design and installation compliance and allow the designer to either 'rectify' the problem or issue a proper variation.
The second part would only be carried out once the building is fully ready for occupation and design and installation and 'first stage commissioning certificates, and all drawings and users documentation are available. The commissioning engineer should then go through all the documentation and carry out further inspections and tests and only then issue a final commissioning certificate. (this is similar but not quite the same as an 'acceptance' certificate') hopefully this final commissioning certificate could confirm that there are no 'variations' whatsoever other than pre-agreed variations
The system currently used does not fit in with how projects are run. Buildings and projects are only finally completed hours before handover to the customer (so that payment can be released) and many of the elements of fire alarm commissioning have been completed days or weeks before (at the insistance of the commissioner's customer) and has probably been altered/damaged since the system was 'commissioned'.