I have just dealt with a medium sized sheltered housing scheme.
The fire alarm has recently been replaced and upgraded to L2 standard and the emergency lighting has been completely overhauled. Furthermore the scheme has had new fire doors installed over a period of 18 months.
Couple this with the fact it has been recently redecorated, and new kitchens are being installed on a rolling schedule for the residents it all seemed at first glance to be a well maintained and managed scheme.
Over the years however (and in particular during the modernisation works) new services have been installed around the property that have not been properly fire stopped.
Huge holes / apertures have been formed within service risers to accomdoate services that dissapear into adjacent flats all around the scheme. A cursory look above the ceiling tiles revealed a similar story in the void.
Because the scheme is riddled with several service ducts and risers which link different parts of the building with one another the building is effectively a large cullinder. Not the best recipe for a stay put policy.
My biggest suprise was to find that the fire alarm contractor had failed to provide fire stopping around his cables.
The responsible person was gutted when I pointed out the problems I'd found - she thought I would be thoroughly impressed by her new fire alarm system, emergency lighting and fire doors. And for the most part I was, they had tried their upmost to be compliant.
It just goes to show that if you don't have suitable compartmentation the fire safety strategy falls down pretty quickly, and that's regardless of how new or advanced your fire alarm system may be, or how well your shiney new fire doors shut tightly.