The enhanced business is due to the fire/water spray tests that soft skinned cables did not meet . To my knowledge certain soft skinned cables have now met this , you would have to check with the manufacturer .
There are still some areas that you need to watch on the soft skinned cable side , ie drops to call points need to be mechanically protected is there is a risk to be damaged , obviously the mineral can take a knock.
We had problems in the early days on addressable due to capacitance on mineral , but that has long since gone.
Buzz's comment is spot on as this one usually is not forthcoming , you need to quantify this as a must.
I would factor a sum in because I have seen numerous cross polarities and identify phase tape lost on change overs , additions so be careful when you start breaking in.