Scenario:
Large L-shaped building over G-4th floor c1974.
Recently fully refurbished for multi letting (was owned & used by one company, who sold it and leased back some of the space)
Main stair has 2 passenger lifts in it & a part atrium (open from ground reception area to 1st level) and new FD30s doors into floorspace.
For travel distance and occupancy levels at each end of the wings there is a fire stair to final exit with original Fd30 doors and rebates - but right next to these are the openings of another lift shaft onto the open floorspace, no protection.
This doesn't look quite right & I suspect that the lifts may have originally been in a lobby off the fire stairs, backed up by one refurbished floor still having a lobby.
So you have large open floors with two different unprotected shafts into them right next to the fire stairs.
I tried to dig out the old fire cert to look for lobbies but it wasn't on site.
There is little compensation and the fire alarm people have lowered the cover with their new install - previously all the motor rooms and basement plant and switchgear plus several of the floors had DS or DH - now there is only detection to the boiler, none of the switch-rooms, the old motor room & floor DS is either gone or left in unconnected and the only other AFD is a smoke head within 1.5m of most (but not all) lift openings plus a half finished head to one fire stair landing
As a multi-occupancy with different parts occupied at different times (so manual alarm not reliable) I'm looking at restoring lobbies and/or increasing detection
What I'm wondering is if the refurb didn't go through the BCO and that lobbies have been removed??