Buzz If I have well understood your question, any fire alarm system is designed to support a limited number of sounders... isn't?
In your case your system is designed to support a number of normal sounders per sounder circuit call it 'Xn', with a unit current consumption call it 'In'.
How ever, if replacing the normal sounders by IS (Intrinsically Safe) ones the new unknown number call it 'Xis', these later should have a Unit current consumption of 'Iis'
Where:
Xn: well defined through manufacturer instruction Guide
In: well defined through manufacturer instruction Guide
Iis: well defined through manufacturer instruction Guide
Xis: Unknown
Therefore:
Xn ---------------> In
Xis ---------------> Iis Then: Xis = (Xn * Iis)/In = Number of IS sounder required
Hope this help, and please forgive my ignorance, if I am away from the main subject