Author Topic: Kentec AS Panels  (Read 13436 times)

Offline GregC

  • Full Member
  • ***
  • Posts: 180
Kentec AS Panels
« on: September 11, 2008, 11:33:26 AM »
Got a small problem with some we have recently fitted, it appears the biggest battery you can squeeze in is a 7Ah, minimum Kentec advise is a 9Ah.

Anyone know where we can get 12v 9ah batts ?

It seems absurd that a panel with 3 No. Xp95 Xpanders only on the loop is going to need a seperate battery box to comply with BS.

Max dimensions of the battery that will fit are

151mm long - this isnt to critical
94mm high - cannot be any higher
86mm deep - cannot be any bigger

I tried all the usual suppliers but they seem to jump from 8Ah to 10Ah which is to big, i even looked at 4 x 6v batts but again to deep.

Anyone come across this before and have a solution that doesnt involve a battery box?

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Kentec AS Panels
« Reply #1 on: September 11, 2008, 12:52:42 PM »
Quote from: GregC
Got a small problem with some we have recently fitted, it appears the biggest battery you can squeeze in is a 7Ah, minimum Kentec advise is a 9Ah.

Anyone know where we can get 12v 9ah batts ?

It seems absurd that a panel with 3 No. Xp95 Xpanders only on the loop is going to need a seperate battery box to comply with BS.

Max dimensions of the battery that will fit are

151mm long - this isnt to critical
94mm high - cannot be any higher
86mm deep - cannot be any bigger

I tried all the usual suppliers but they seem to jump from 8Ah to 10Ah which is to big, i even looked at 4 x 6v batts but again to deep.

Anyone come across this before and have a solution that doesnt involve a battery box?
Did Kentec know, that only 3 Xpanders in the loop, is it on that basis they said a set of 9Ah is required?

Why don't you do your own battery calculation, according to the load you have, you may find less Ah required?

In the worst case, there is no escape from a cheap battery box! :)

Offline GregC

  • Full Member
  • ***
  • Posts: 180
Kentec AS Panels
« Reply #2 on: September 11, 2008, 01:14:41 PM »
Sorry, should have explained a bit more.

The Synchro panel itself requires a 9Ah battery to give 24 hours standby, its in their data sheet

A 7 Ah that is the biggest that we can source that will fit in the panel and that is only good for 21 hours.

This is without anything connected to the loops or sounders or relays etc.

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Kentec AS Panels
« Reply #3 on: September 11, 2008, 01:47:36 PM »
Having done the calcs myself:

Each Apollo expander is 20mA in quiecent and in alarm, therefore 60mA

If it s a 1 loop panel then quiecesnt of a loop card is 105mA, with it being 180mA in alarm.

Therefore for a 1 loop panel with 3 xpanders you would need 7Ah batteries (conversion equates to approx 5.2Ah req) and a 2 loop panel you would need 7Ah batteries(conversion equates to approx 6.9Ah)

These calculations are based on only these xpanders and nothing else connected with 24 hour standby.
** Knowledge is power, I'm still working on both **

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Kentec AS Panels
« Reply #4 on: September 11, 2008, 03:17:00 PM »
Quote from: GregC
Sorry, should have explained a bit more.

The Synchro panel itself requires a 9Ah battery to give 24 hours standby, its in their data sheet

A 7 Ah that is the biggest that we can source that will fit in the panel and that is only good for 21 hours.

This is without anything connected to the loops or sounders or relays etc.
If Kentec data sheet said 9Ah is a minimum requirement, and designed a panel box that doesn't fit 9Ah...,

How it sounds?

Unless they manufacture their own 9Ah that fit their own panel, and in that case order it from them :)

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Kentec AS Panels
« Reply #5 on: September 11, 2008, 03:22:53 PM »
Creg;

Why not display your quote in here and lets see, what battery capacity is required.

Need to know how many of each device used : Detectors, sounders, EOLs.... etc

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Kentec AS Panels
« Reply #6 on: September 11, 2008, 04:16:08 PM »
Loads of them brand new on ebay
Its time to make a counter attack !

Offline John Dragon

  • Full Member
  • ***
  • Posts: 189
Kentec AS Panels
« Reply #7 on: September 11, 2008, 06:14:20 PM »
The MAXIMUM Kentec advise is 9Ah   (chapter 23.4, page 31 of AS product manual).
The std size we use in nearly all installations is 7Ah.

Graeme

  • Guest
Kentec AS Panels
« Reply #8 on: September 11, 2008, 08:58:34 PM »
I'm sure EMS panels come with 9ah. I will find out name for you tomorrow.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Kentec AS Panels
« Reply #9 on: September 11, 2008, 09:00:28 PM »
Quote from: GregC
Got a small problem with some we have recently fitted, it appears the biggest battery you can squeeze in is a 7Ah, minimum Kentec advise is a 9Ah.

Anyone know where we can get 12v 9ah batts ?

It seems absurd that a panel with 3 No. Xp95 Xpanders only on the loop is going to need a seperate battery box to comply with BS.

Max dimensions of the battery that will fit are

151mm long - this isnt to critical
94mm high - cannot be any higher
86mm deep - cannot be any bigger

I tried all the usual suppliers but they seem to jump from 8Ah to 10Ah which is to big, i even looked at 4 x 6v batts but again to deep.

Anyone come across this before and have a solution that doesnt involve a battery box?
Try this:

12V 9AH Battery PPO400
Dimensions: 4" Height x 2.54" Width x 5.95" Depth ---->   101mm x 64.5mm x 151mm
Output Voltage: 12V DC - Product Type: Battery Unit - Capacity: 9Ah - - ...More BAT-0489

The link is:

http://www.provantage.com/eaton-powerware-bat-0489~4POWA002.htm

Offline John Dragon

  • Full Member
  • ***
  • Posts: 189
Kentec AS Panels
« Reply #10 on: September 11, 2008, 09:35:23 PM »
Missing the point, folks, the MAX battery size is 9Ah not the Min battery size!

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Kentec AS Panels
« Reply #11 on: September 11, 2008, 09:47:58 PM »
Quote from: John Dragon
Missing the point, folks, the (MAXIMUM) battery size is 9Ah not the Min battery size!
And

Quote from: Creg
Got a small problem with some we have recently fitted, it appears the biggest battery you can squeeze in is a 7Ah, (MINIMUM) Kentec advise is a 9Ah.
What is shown on Kentec Datasheet?

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Kentec AS Panels
« Reply #12 on: September 11, 2008, 09:52:43 PM »
Kentec cannot possibly make a statement saying 2 x 9Ah batteries will support 24 hour standby... This is the maximum size for the standard enlosure... You need to calculate the standby required based upon the loop loading.
** Knowledge is power, I'm still working on both **

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Kentec AS Panels
« Reply #13 on: September 12, 2008, 04:03:33 PM »
Quote from: Big_Fella
Kentec cannot possibly make a statement saying 2 x 9Ah batteries will support 24 hour standby... This is the maximum size for the standard enlosure... You need to calculate the standby required base dupon the loop loading.
True but they can if they have calculated for absolute maximum load on a given panel....

But apart from that.....

Graeme is right, 9Ah batts are available through EMS... and they are the same size as 7Ah only difference is the spade connections are larger and don't fit standard panel tails - I still haven't been able to source them from anywhere else.

Be aware the ones Benz has found look physically bigger than 7s and may not be a direct replacement.

You can always order the AS panel in the bigger enclosure (M3 from memory i believe) into which you can get 12Ah....
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline GregC

  • Full Member
  • ***
  • Posts: 180
Kentec AS Panels
« Reply #14 on: September 16, 2008, 09:26:55 AM »
Thanks for the replies.

The data sheets says 9Ah 12v x2, no max or min.

The load we have and what the control panel requires means a 7Ah will only last for 21 hours, technical support at Kentec has advised this is correct and the panel requires a 9Ah battery for 24 hours standby.

With hindsight I would have ordered the larger enclosure and put in the 12's but was a bit miffed to not be able to readily source batteries off the shelf for a standard control panel.

Thanks for the pointer to ebay but personnally I wouldnt feel comfortable fitting ebay batts into a fire alarm.

I am waiting for the supplier of the panel to get back in touch with an answer.