It is 1 when the system alarm load is equal or less than 1/20th of the battery's stated capacity. It is 1.75 when the battery's alarm load is greater than 1/20th of the battery's staed capacity.
If: Alarm load <= C/20 -------> D=1
But BFPSA said:
( For some systems the alarm load is quite low, perhaps nearly equal to the standby load. In this case the battery is not stressed and factor D=1. This can make a small reduction to the calculation battery capacity. )
If: Alarm load = Stand by load = I1 T1, and (Not = C/20) -----> D=1
The difference is: you are comparing the Alarm load with the 1/20th of full battery capacity = ‘C/20’, in order to set D=1. And BFPSA are comparing Alarm load with the standby load = I1 T1, In order to set D=1.
It is the same answer only when setting D=2 for BFPSA and D=1.75 for BS.
When alarm load > (design load = C/20)
This is what justifies what I said: (This is QUITE different to what wiz mentioned about) BS version:
Also you keep saying the same thing with a negation way:
You will find that much of what I have previously been explaining to you, you have now suddenly uncovered in your BFPSA book. Therefore it certainly is not QUITE different.
Finally I said (the cup is half empty) and you said (the cup is half full), sort of…etc
I am not rubbishing your advice Wiz, I am trying to decipher what you said, in a (No winner and No loser fashion), I just feel happy, only when I learn some thing new from any one…, or when some one say, your answer was useful and informative to me…etc, and that’s it
Have a nice day