My concern with wireless stuff is; say a survey proved more than 70% of signal strength.
1. Would that be the only requirement to start the first fix in that proved area?
2. How can you tell there are no other interferences around?
3. How can you tell if the signal strength detected at time 'T' would be the same 24/7?
4. How can you tell if interferences have minor effects at time ‘T’, they will remain minor for 24/7?
1. yes... if the survey kit is telling you the strengths are ok then what is there to stop you.....??
2. You can't.... If its a new build you can expect signals to change with plasterboard going up, ducting and services going in etc.... and it'd very hard to take these things into account.
3. You can't.... we've had signal strengths effected by scaffolding around the outsides of buildings and basements effected by cars parking on roads above....
4. Not sure what is a "minor" effect is... the above scenarios may prevent signals call in signals from being seen by an EMS panel within the two hour window however a fire signal would be seen. EN54 systems are different and I don't know how they would react.... good question...!!