I know the provision of extinguishers is subject to risk assessment but this will be done following occupation.
Has anyone any views regarding this provision as I consider them to be inappropriate.
As you have already said a FRA should be carried out to ascertain the risks on the premises and whether extinguishers would be required and what type. In the type of establishment you have mentioned unless they have a specific requirement for 9kg Powder Extinguishers then I would suggest removal and replacement for extinguishers more suited to the environment. I would normally suggest as a guide 1 x 6Litre Foam (or a 6 Litre Water Extinguisher which has passed the 35Kv conductivity test) and 1 x 2kg CO2 Extinguisher for every 200m/sq with a minimum of two pairs on each floor (assuming each floor would not be more than 400m/sq and that there were no uncovered risks).
This really is just a guess without seeing the premises. This would ensure compliance with BS 5306 Part 8 and would also ensure that the bean counters are happy.
Extract from BS5306 Part 8 2000
6.2 Class A fires in carbonaceous solids
Class A materials are generally present in all premises and occupancies. ...............................
The discharge of a powder extinguisher in a confined space can cause a sudden reduction of visibility which
may temporarily jeopardize escape, rescue or other emergency action. For this reason water-based
extinguishers are to be preferred in hospitals, old people's homes and hotels.
I would also suggest powder extinguishers are unsuitable for a "Learning Disabilities residential unit"
Are DP extinguishers not the most expensive?
They shouldn't be the most expensive but a lot depends on who you buy them from. Also cost shouldn't really come into the equation as the customer should really look at what is the right solution.