Author Topic: Inergen system  (Read 19927 times)

Davo

  • Guest
Inergen system
« on: November 25, 2008, 03:41:10 PM »
Advice please

Three inner rooms, 97 sq m, 80 sq m and 30 sq m
One gas store 8 sq m

1) how many cylinders are likely
2) will there be a need for external blast vents as on another site with FM200


davo

out of his depth :D

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Inergen system
« Reply #1 on: November 25, 2008, 04:36:23 PM »
There is always a need for pressure release vents with inergen. It works by pushing enough air from the room out of the vent and replacing it with a the inergen mix to bring the oxygen concentration below that which will support combustion.

You could do your sums- inergen cyls are charged to 300 Bar! The cylinders must not be in the protected room- how many seperate installations are you having?

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Inergen system
« Reply #2 on: November 25, 2008, 09:55:19 PM »
Davo- this is a guide only. The systems will need to be calculated.

Inergen comes in a range of cylinder sizes. 27, 40, 67, 80 litres.

The typical volume covered  at 51% concentration is  16, 23, 39, 47 cubic metres respectively. The big 80 litre cylinders are 1760mm high and 267mm diameter.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Inergen system
« Reply #3 on: November 25, 2008, 11:20:27 PM »
Advice please

Three inner rooms, 97 sq m, 80 sq m and 30 sq m
One gas store 8 sq m

1) how many cylinders are likely
2) will there be a need for external blast vents as on another site with FM200


davo

out of his depth :D
Hi Davo - I take it you mean cubic metres?
« Last Edit: November 25, 2008, 11:22:45 PM by Buzzard905 »

Offline Ashley Wood

  • Sr. Member
  • ****
  • Posts: 253
    • http://www.thermatech.uk.com
Re: Inergen system
« Reply #4 on: November 26, 2008, 10:08:59 AM »
Don't forget to alow for the weight of the cylinders and make sure that the contractor secures the pipes well. Also, you can't just vent pressure into the corridors or another room.

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Inergen system
« Reply #5 on: December 02, 2008, 11:40:20 PM »
Advice please

Three inner rooms, 97 sq m, 80 sq m and 30 sq m
One gas store 8 sq m

1) how many cylinders are likely
2) will there be a need for external blast vents as on another site with FM200


davo

out of his depth :D


Davo ,
Why Inergen ?
Its time to make a counter attack !