Author Topic: Fire Protection to Service Corridors in Shopping Malls  (Read 6159 times)

Offline SidM

  • Jr. Member
  • **
  • Posts: 92
Fire Protection to Service Corridors in Shopping Malls
« on: December 04, 2008, 04:37:16 PM »
In shopping mall with individual units having their own escape at the rear in to a service corridor, is there a need to have lobby protection between the unit and the service corridor.  If so, how important is it to keep the lobby area clear considering that in the mall area there is smoke extraction and possibly even sprinklers.
"We are the unwilling,
Led by the unqualified,
Doing the unnecessary,
For the ungrateful.
-Living the dream!"

Offline Harry11

  • Newbie
  • *
  • Posts: 11
Re: Fire Protection to Service Corridors in Shopping Malls
« Reply #1 on: December 04, 2008, 04:50:24 PM »
BS 9999. E.3.1.4 Offers comprehensive guidance.


Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Fire Protection to Service Corridors in Shopping Malls
« Reply #2 on: December 04, 2008, 09:24:19 PM »
Yes there is a need. The lobby is to limit the amount of smoke that enters the corridor. This is especially important where the corridor is a dead end. There is also generally 120 minutes compartmentation between the units and the service corridors.

It is very important to keep it clear as it is the escape route for persons in that unit in the event of a fire in that unit, and also in the event of a fire in a nearby/opposing unit that may mean people do not want to or can't escape into the mall.
« Last Edit: December 04, 2008, 09:27:33 PM by CivvyFSO »

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Fire Protection to Service Corridors in Shopping Malls
« Reply #3 on: December 05, 2008, 08:34:48 AM »
We have always designed such systems with lobby protection, which includes automatic detection
** Knowledge is power, I'm still working on both **

Offline Dinnertime Dave

  • Hero Member
  • *****
  • Posts: 819
Re: Fire Protection to Service Corridors in Shopping Malls
« Reply #4 on: December 08, 2008, 01:36:31 PM »
You can use smoke extraction instead to keep the corridor clear

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: Fire Protection to Service Corridors in Shopping Malls
« Reply #5 on: December 09, 2008, 12:39:34 PM »
If theres stuff in your lobby then it aint a lobby any more.

Part 10 / 9999 is a bit OTT on some of this stuff so if it's small then it may not be such an issue. Although I'm not sure how you are keeping your escape route clear if its full of stuff???