Author Topic: Maintenance Visit  (Read 6375 times)

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Maintenance Visit
« on: December 16, 2008, 10:26:21 PM »
I am under the impression that a yearly 100% visit on a fire system is not compliant unless you go back and check the standby batteries on a separate visit , am I right or am I getting old and my brain needs updating to Vista  ::)
Its time to make a counter attack !

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Maintenance Visit
« Reply #1 on: December 16, 2008, 11:07:27 PM »
Yes Galeon, you are right.
Whilst some items only have to be tested only annually, others have to be tested on every visit and the maximum period between visits is six months (although the period can, and might have to, be less (depending on assessment))

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Maintenance Visit
« Reply #2 on: December 16, 2008, 11:31:22 PM »
am I right or am I getting old and my brain needs updating to Vista  ::)

No dont do that- look what happened to Benz when he upgraded. He talks in riddles and has lost all his data- as a final backup he  has written down all he knows about fire alarms in his new book. Trouble is its just a front cover.

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Re: Maintenance Visit
« Reply #3 on: December 17, 2008, 04:18:33 AM »
The answer to that Kurnal , is DOS not to keen on grafting anymore , tired out from pushing the granddaughter around.
Its time to make a counter attack !

Offline Thomas Brookes

  • Sr. Member
  • ****
  • Posts: 290
Re: Maintenance Visit
« Reply #4 on: December 17, 2008, 07:33:28 AM »
Got to be 2 visits per year.

Can not wait for Benz book
I refuse to have a battle of wittts with an unarmed person.

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Maintenance Visit
« Reply #5 on: December 17, 2008, 08:27:27 AM »
Indeed a minimum of 2 visits per year. 

Although when offering a maintenanc contract you need to take into consideration the environment etc, detectors may need cleaning fairly often to prevent false alarming etc, providing this is a good maintenance regime for the client.
** Knowledge is power, I'm still working on both **