Thanks Jokar.
The wording is as follows (extracts only)
Following an audit.....the following requirements of the order have not been adequately met and should be addressed in your fire risk assessment. A time specific corrective action plan should be produced to address the followingduties that are statutory requirements of the Order.
The Responsible Person must ensure equipment and devices for use by, or for the protection of Fire Fighters are maintained in an efficient state, in working order and in a good state of repair (specifically the Sprinkler System) (Article 38(i))
..........As a guide ....the work should be completed within 3 months........A further visit will be made on or after 1 March 2009 to ensure that the requirements of the schedule have been carried out.
I must stress that means of escape are appropriate and the sprinklers were only ever installed as a result of the local enactment in respect of storage buildings larger than 7000m3 which only apply in a few areas of the UK. Under latest design codes- BS9999, ADB 2006 etc this warehouse would be deemed satisfactory without sprinklers if it were built 1/2 mile down the road in the neighbouring county.