Author Topic: Escape lifts in Hospitals- HTM 05-03 part e Vs BS9999  (Read 6262 times)

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Escape lifts in Hospitals- HTM 05-03 part e Vs BS9999
« on: January 13, 2009, 05:19:59 PM »
Is it reasonable to apply the risk assessment approach to the use of conventional lifts for evacuation purposes as outlined in BS9999 in existing hospitals? Or should we stick to the HTM and only consider the use of escape lifts in an emergency?

Offline Colin Newman

  • Full Member
  • ***
  • Posts: 114
    • Healthfire
Re: Escape lifts in Hospitals- HTM 05-03 part e Vs BS9999
« Reply #1 on: January 13, 2009, 06:03:53 PM »
In my opinion the use of conventional lifts for evacuation in hospitals is perfectly valid providing that the approriate risk assessments are undertaken and any necessary measures are set in place.   Due to the size and relative complexity of hospital buildings there are often circumstances when perfectly functioning lifts and thier power supplies, controls etc. are remote both physically and in terms of fire protection from any fire incident and could continue to operate safely.

HTM 05-03 Part E addresses the specific issues and appropriate measures when vertical evacuation of patients using lifts is considered as part of the evacuation startegy.  Usually this approach is take when either there are insufficient stair provisions or when a particular need has been identified such as a limited potential for horizontal evacuation particularly if it involves the evacuation of ITU.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Escape lifts in Hospitals- HTM 05-03 part e Vs BS9999
« Reply #2 on: January 14, 2009, 06:20:52 PM »
Thanks for your help Colin