Author Topic: 60/65 db too loud for disabled refuge system?  (Read 17173 times)

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
60/65 db too loud for disabled refuge system?
« on: February 24, 2009, 12:07:44 PM »
The disabled refuge communication system installed has in-built noise cancelling circuitry to try and ensure the clearest speech communication possible.

However this noise cancelling circuitry cannot cope with the background noise of the fire alarm sounders thereby making the speech unintelligible!

Anyone had anything similar?

Could it be argued that the recommended fire alarm sound level could be reduced in the disabled refuge areas, as a BS variation, to allow speech to be understood?

Could it be argued that the disabled refuge communication system should only be used after the fire aalarm sounders have been silenced anyway?

Whadyafink?

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: 60/65 db too loud for disabled refuge system?
« Reply #1 on: February 24, 2009, 12:12:01 PM »
I've had a lot of new builds over the last 12 months where they have accepted that a sounder is not provided in this area, but just a beacon for visual indication.  Therefore overcoming the problem
** Knowledge is power, I'm still working on both **

Graeme

  • Guest
Re: 60/65 db too loud for disabled refuge system?
« Reply #2 on: February 24, 2009, 12:17:29 PM »
The disabled refuge communication system installed has in-built noise cancelling circuitry to try and ensure the clearest speech communication possible.

However this noise cancelling circuitry cannot cope with the background noise of the fire alarm sounders thereby making the speech unintelligible!

Anyone had anything similar?

Could it be argued that the recommended fire alarm sound level could be reduced in the disabled refuge areas, as a BS variation, to allow speech to be understood?

Could it be argued that the disabled refuge communication system should only be used after the fire aalarm sounders have been silenced anyway?

Whadyafink?

I'm guessing that if the BS has a reduction for areas where people summon for the fire brigade over the phone then the DDA would find a way that the same right should be afforded to a wheel chair person summoning for help over a refuge system.


Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: 60/65 db too loud for disabled refuge system?
« Reply #3 on: February 24, 2009, 12:55:01 PM »
What about alternation between 'the disabled refuge communication system' and 'alarm sounders', if the disabled area is not separate, an external relays may have to be used to switch OFF the sounders for the short periods while the speakers are ON and vise versa..., but I don’t know if this is acceptable by BS…

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: 60/65 db too loud for disabled refuge system?
« Reply #4 on: February 24, 2009, 01:26:40 PM »
There is a particular manufacturer I know of that has a volt free output in each of the remote call stations.  This is operated when the remote call station is activated by the user.  Not sure if this is common across other manufacturers?

But on an addressable system you could feed this into an input module to isolate a particular sounder.  Although isolating a sounder when the system is already in alarm may prove difficult.  Actually this isnt something I have personally tried.  Is this even possible?
** Knowledge is power, I'm still working on both **

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: 60/65 db too loud for disabled refuge system?
« Reply #5 on: February 24, 2009, 01:48:27 PM »
Technically yes; it is possible but, I am not sure if BS accept stopping the sounders for some reasons like this.. or other reasons

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: 60/65 db too loud for disabled refuge system?
« Reply #6 on: February 24, 2009, 05:49:57 PM »
I would not have a problem with reduced sounder levels in staircases as a sensible variation in the circumstances described.
You can never write general rules on when the fire alarm may be silenced. It can be silenced when it has served its purpose- and all persons are safely accounted for. For example in a care home you may write special rules allowing the alarm to be silenced but not reset when all staff have responded.

You could also argue that as the emergency communication device is usually next to the fire alarm panel, the responsible person could temporarily silence the alarm to use the comms device if he thought it would help, but this may confuse persons still evacuating and some may turn round and re-enter the building.

The best solution is to ensure that persons in refuges receive an early visit and support of a fiire warden and offered whatever assistance is needed. But its a very good point you raise Dr Wiz and we must never forget what it must feel like to be stuck by yourself in a wheelchair in the upper floors of a building on fire, and everyoune else walking out.
« Last Edit: February 24, 2009, 06:30:39 PM by kurnal »

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: 60/65 db too loud for disabled refuge system?
« Reply #7 on: February 24, 2009, 06:24:47 PM »
I think going along the lines of relays on refuge systems and more I/O units and cause and effect programming etc in order to silence one or two sounders in the locality of the refuge point when it's in use is just over complicating the system.

I'd go with the reduction of alarm levels in the area....
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline dark one

  • Newbie
  • *
  • Posts: 25
Re: 60/65 db too loud for disabled refuge system?
« Reply #8 on: February 24, 2009, 07:11:56 PM »
I would go with a beacon in this area as the sounders have already acheived there goal and the person has evacuated to the refuge.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: 60/65 db too loud for disabled refuge system?
« Reply #9 on: February 24, 2009, 09:57:23 PM »
What about beacons and speakers throughout, and no sounders at all

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: 60/65 db too loud for disabled refuge system?
« Reply #10 on: February 24, 2009, 10:12:42 PM »
Having a voice alarm or even voice enhanced sounders I think would prove a costly increase, as 99% of new builds have the requirement for disabled refuge stations now.

I think the idea of beacons only at the refuge point is a good compromise, giving the user a good viable system
** Knowledge is power, I'm still working on both **

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: 60/65 db too loud for disabled refuge system?
« Reply #11 on: February 25, 2009, 09:31:00 AM »
Thanks for all the comments and opinions.

For everybody's information, there is no alarm sounder in the disabled refuge area, however the sound level is still at 63db in this area, and this is enough to affect the quality of the disabled access refuge communication system in use. The alarm sound level has to be reduced to 50 db before the interference is reduced sufficiently to allow the speech communication to work satisfactorily.

I feel that the technical solutions to provide automatic or manual alarm sound level reduction only when the speech communication system is used are potentially too expensive or add possible confusion to how the system would work.

In the circumstances we will seek a variation to reduce the alarm sound levels in this area but also provide an alarm visual warning beacon. We will also talk with the communication system manufacturer further and maybe they can adapt the design of their equipment to reduce this problem in future installations.
« Last Edit: February 25, 2009, 09:32:49 AM by Wiz »

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: 60/65 db too loud for disabled refuge system?
« Reply #12 on: February 25, 2009, 07:38:34 PM »
Dr Wiz
In the situation you describe the noise level both in the refuge and at the control panel may make it difficult to communicate from either end. Alternatively the intercom system may amplify the alarm sound more than the voice frequencies and add to the problem. 

There are frequency specific attenuators available exactly for this purpose. When I worked on a fire control room project we had a common problem that the 999 operators could not hear the message and also suffered discomfort because of the sound of the alarm feeding into their headsets, the filters were very effective at controlling this.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: 60/65 db too loud for disabled refuge system?
« Reply #13 on: February 26, 2009, 09:51:51 AM »
Good call Prof. That is exactly the type of thing that the manufacturers will be asked to look at. The problem is where the alarm sound uses lots of frequencies and so any masking circuitry will then mask those frequencies of normal speech as well.

As an alternative I am considering a morse code disabled refuge communication system using large filament lamps as the indicators. Obviously, all disabled users, management staff and attending fire service officers will have to be trained in Morse code, but we see this as a small price to pay for the benefits provided ;)

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: 60/65 db too loud for disabled refuge system?
« Reply #14 on: February 26, 2009, 07:06:39 PM »
-/..../.-/-/...//     .-   //  --./---/---/-..//    ../-.././.-//