Have seen and heard several times, about sites under construction, having temporary and rough fire alarm systems with cables hanging throughout, is there any specific fire alarm system's standards, to be applied to any site under construction?

Also, I have heard of fire accident which caused death and damage, i.e. in Dubai and China... etc, and the fire occured while the building was under construction. What are the standards applicable in UK, in this matter?

« Last Edit: March 04, 2009, 07:42:09 PM by Benzerari »

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Sites under construction, what standards?
« Reply #1 on: March 04, 2009, 07:55:38 PM »
Sites I've seen 'currently' under construction have only always had rotary bells along with extinguishers.

Site cabins may have some kind of basic system, i.e. break glasses smoke sensors/sounders, but apart from that, I cannot recall anything more.

** Knowledge is power, I'm still working on both **

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Sites under construction, what standards?
« Reply #2 on: March 04, 2009, 07:58:53 PM »
Its all a bit of a mess Benz.
The Construction Design and Management (CDM) Regulations apply to most building projects.

There are fire safety regulations within the  (CDM) Regs- Regulations 38 - 41. The CDM Regs identify duty holders in a completely different way to the Fire Safety Order - defining roles such as clients, designers, co-ordinators, principal contractors etc.

There is an ACOP setting out how the CDM regs should be implemented. Its available from ther HSE – L144. The ACOP addresses issues such as temporary measures for raising the alarm on fire during the constructon phase where in the main the only persons at risk are the builders and whilst few of the structural precautions are in place generally fire loading in the building is also low. (I said generally!!!!) Theres another more practical older guidance document HSG168.

On the other hand the Fire Safety Order applies to all places including building sites. The Fire Safety Order  is enforced by the HSE on a building site that is fully self contained and secure. Where the site is part of a complex with other occupiers in addition to the site personnel eg updating of a retail unit in a  shopping centre, then the  Fire Safety Order is enforced by the Fire Authority.

The Construction Design and Management (CDM) regs mirror this and on sites where the fire Authority are the enforcement Authority under Fire Safety Order  they are also responsible for enforcement of the CDM Regs 38- 41 ( see Regulation 46- Enforcement)

Under the Fire Safety Order the Responsible Persons (RP), must carry out risk assessments to protect relevant persons. In a building with multiple employers each RP must cooperate and communicate and carry out a risk assessment in so far as he has control.

The CDM Regs identify duty holders in a completely different way to the Fire Safety Order- defining roles such as clients, designers, co-ordinators, principal contractors etc. Some CDM duty holders may be extremely difficult to pin down as Responsible persons under the Fire Safety Order.

Nationally I dont think the Fire Authorities appear to be aware or equipped to deal wth their enforcement duties under the CDM regs. Whilst the CDM duties and Health and Safety planning process appear to be working well on sites I think its all a terrible mess in terms of the Fire Safety Order.

And  apart from some general guidance published by the FPA there appears to be no national guidance  guidance available on the application of the Fire Safety Order to building sites and benchmark  standards to be applied. Hence the more relevant and available guidance- that issued under the CDM ACOP - tends to be more common. Trouble is it does not effectively protect all persons who may be at risk in the event of a fire- it only focusses on site workers and not passers by for example.
« Last Edit: March 04, 2009, 08:06:37 PM by kurnal »

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: Sites under construction, what standards?
« Reply #3 on: March 04, 2009, 08:16:46 PM »
Its all a bit of a mess Benz.
The Construction Design and Management (CDM) Regulations apply to most building projects.

There are fire safety regulations within the  (CDM) Regs- Regulations 38 - 41. The CDM Regs identify duty holders in a completely different way to the Fire Safety Order - defining roles such as clients, designers, co-ordinators, principal contractors etc.

There is an ACOP setting out how the CDM regs should be implemented. Its available from ther HSE – L144. The ACOP addresses issues such as temporary measures for raising the alarm on fire during the constructon phase where in the main the only persons at risk are the builders and whilst few of the structural precautions are in place generally fire loading in the building is also low. (I said generally!!!!) Theres another more practical older guidance document HSG168.

On the other hand the Fire Safety Order applies to all places including building sites. The Fire Safety Order  is enforced by the HSE on a building site that is fully self contained and secure. Where the site is part of a complex with other occupiers in addition to the site personnel eg updating of a retail unit in a  shopping centre, then the  Fire Safety Order is enforced by the Fire Authority.

The Construction Design and Management (CDM) regs mirror this and on sites where the fire Authority are the enforcement Authority under Fire Safety Order  they are also responsible for enforcement of the CDM Regs 38- 41 ( see Regulation 46- Enforcement)

Under the Fire Safety Order the Responsible Persons (RP), must carry out risk assessments to protect relevant persons. In a building with multiple employers each RP must cooperate and communicate and carry out a risk assessment in so far as he has control.

The CDM Regs identify duty holders in a completely different way to the Fire Safety Order- defining roles such as clients, designers, co-ordinators, principal contractors etc. Some CDM duty holders may be extremely difficult to pin down as Responsible persons under the Fire Safety Order.

Nationally I dont think the Fire Authorities appear to be aware or equipped to deal wth their enforcement duties under the CDM regs. Whilst the CDM duties and Health and Safety planning process appear to be working well on sites I think its all a terrible mess in terms of the Fire Safety Order.

And  apart from some general guidance published by the FPA there appears to be no national guidance  guidance available on the application of the Fire Safety Order to building sites and benchmark  standards to be applied. Hence the more relevant and available guidance- that issued under the CDM ACOP - tends to be more common. Trouble is it does not effectively protect all persons who may be at risk in the event of a fire- it only focusses on site workers and not passers by for example.


Thanks for this info Kurnal;

If there is no national guidance available on the application of the FSO to building sites and standards to be applied, do you think because UK hasn't yet experienced loss of lifes and properties while the building is still under construction, like other emerging countries?


Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Sites under construction, what standards?
« Reply #4 on: March 04, 2009, 08:33:02 PM »
There have been some very significant fires on building sites though Benz, although perhaps no major loss of life.

http://news.bbc.co.uk/1/hi/england/london/5173808.stm

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Sites under construction, what standards?
« Reply #5 on: March 05, 2009, 12:07:32 AM »
I have asked a few construction company project managers and they don't seem particularly aware that the Fire Safety Order applies, and they seem to think they have covered all their duties with the 3 specific articles of the CDM regs.

The HSE probably care very little as they have many more things to worry about, like the many lives that are lost during construction by other means. It would be a bad use of resources to all of a sudden direct people towards fire safety on construction sites when more than 50 people die per year (77 in 2006 from a quick net search) from other incidents.

Fire Authorities do not seem to bothered about construction sites either. At then end of the day a construction site has the same duties under the Fire Safety Order as everybody else, but it might take a death followed by a prosecution before anything else happens, but if the HSE are the enforcers then they may go for it under the CDM regs anyway.

HSE and the Fire Authorites are supposed to target the risk, so unless they start making a risk of themselves then I guess they may remain untouched.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Sites under construction, what standards?
« Reply #6 on: January 07, 2010, 10:29:21 PM »
The HSE has recently issued for consultation updated guidance on fire safety on construction sites, HSG168.

Its very much in early draft stages with no end of mistakes (IMHO)   but if anyone wants to see a copy for comment then please PM me.

I am going to respond via the FIA. One interesting point on which they are seeking ideas is how to prevent major fire spread in the construction phase of timber framed buildings as recently ccurred in London. They are currently looking at how compartmentation could be provided to this end, any ideas welcome. My own view is that such passive measures are not realistic unless we have a hybrid construction method using panels or masonry as well as the timber frame.

But I am going to suggest the method of construction and exposure of adjoining properties during the construction phase be assessed in accordance with BR187 and if there is an unacceptable exposure risk then that timber framed construction is not appropriate due only to fire risk in the construction phase.


Offline hammer1

  • New Member
  • Full Member
  • *
  • Posts: 157
Re: Sites under construction, what standards?
« Reply #7 on: January 10, 2010, 11:21:03 PM »
For those wanting to have a look at the CDM ACOPS

It can be downloaded free..

http://books.hse.gov.uk/hse/public/saleproduct.jsf


Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Sites under construction, what standards?
« Reply #8 on: January 11, 2010, 09:19:23 AM »
You need to search for CDM ACOPS after you have clicked on Hammers link.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline hammer1

  • New Member
  • Full Member
  • *
  • Posts: 157
Re: Sites under construction, what standards?
« Reply #9 on: January 11, 2010, 03:25:23 PM »
For those wanting to have a look at the CDM ACOPS

It can be downloaded free..

http://books.hse.gov.uk/hse/public/saleproduct.jsf



Hopefully this link will direct you more

http://books.hse.gov.uk/hse/public/saleproducts.jsf


Then just go down to the CDM  ACOPS

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Sites under construction, what standards?
« Reply #10 on: January 11, 2010, 07:26:22 PM »
It dont work ham you have to search for it.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline rn976

  • Newbie
  • *
  • Posts: 32
Re: Sites under construction, what standards?
« Reply #11 on: January 14, 2010, 02:27:11 PM »
Just a bit more info, re the FA involvment

In determining responsibility for enforcement of the Regulations consideration must be given to the following

The configuration of the construction site in relation to occupied premises.
The physical separation of the construction site and the occupied premises i.e. space separation.
The fire resistance of separating walls, floors, doors etc between the construction site and occupied premises.
The risk of fire spread between the construction site and the occupied premises.

If the FA are carring out enforcement they should concentrate on the following parts of the site under the Construction (Design and Management) Regulations 2007

•   Regulation 39 – The preparation and implementation of emergency procedures to include the necessary evacuation of all or part of the site. such procedures are to be made known to all persons concerned and be tested at regular intervals.
•   Regulation 40 - Provision of a suitable number of emergency routes and exits (including emergency lighting where necessary) and the maintenance of those routes and exits.
•   Regulation 41 – The provision of suitable firefighting equipment and fire detectors and alarm systems. Such equipment is to be accesible and tested and maintained as appropriate. Personnel on the construction site shall be trained in the use of firefighting equipment.

hope this helps

rn 976



Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Sites under construction, what standards?
« Reply #12 on: January 14, 2010, 03:16:23 PM »
If the FA have responsiblity for enforcement of those parts of the CDM regs, then they also enforce the RRO in the construction site.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Sites under construction, what standards?
« Reply #13 on: January 14, 2010, 06:23:21 PM »
In my opinion the Fire Safety Order is the key most important legislation that should be enforced on Construction Sites, whether by the HSE or Fire Authority. I say this because the CDM Regs do not take into account the safety of people off the site who could be affected by a fire.

The CDM Regs create different dutyholders to the Fire Safety Order.

in my experience when I visit construction sites (I train several construction companies in fire safety)  the dutyholders under the CDM Regs tend NOT to be even aware of the Fire Safety Order. I think (My Opinion only) this is because on those sites where the HSE are responsible for enforcement of the Fire Safety Order they actually only enforce the CDM Regs. This way they only have to liaise and deal with the single set of duty holders for all safety issues under the CDM Regs. 
As a result of my experience with the Industry I believe that  HSE do not consider the Responsible Person or in practical terms enforce the Fire Safety Order.


And the Construction companies get away without considering other relevant persons off the site. Hence Colindale et al.
Now if this is total piffle please correct me. But thats how I see it.

Offline hammer1

  • New Member
  • Full Member
  • *
  • Posts: 157
Re: Sites under construction, what standards?
« Reply #14 on: January 15, 2010, 02:26:49 PM »
http://www.fseonline.co.uk/articles.asp?article_id=9686&viewcomment=1&OmniTest_CampName=fseeditorial-15-01-10&OmniCamp_Name=fseeditorial-15-01-10&OmniWS_Name=Fire%20Safety%20%26%20Engineering%20%28FSE%29%204943.62230-62&OmniWS_ID=3&OmniPR_Name=Newsletter_FSE%20Weekly%20Editorial&OmniPR_ID=3&OmniLink_Label=more&OmniDBG_URN=&OmniDBG_File_ID=&OmniSeg_Code=&OmniCC_Code=&OmniComp_Name=SRM%20LTD&OmniJob_Title=Consultant&Omni_Source=

In regards to considering FSO is the most important legislation for construction sites, I totally dis-agree. From working on many construction sites, there are far more important issues/legislation that are life threatening than the risk to life in the event of fire on construction sites. From a property damage view, obviously the FSO elevates itself, but from a pure life safety view, there are many more high risk activities that need addressing and prioritising before we reach the subject of fire safety.

I have no got the figures by hand, but just have a look at the annual fatalities on construction sites over the last 10 years to give you a understanding of where the HSE target.

I feel if all construction sites follow a robust regime in line with HSG 168 and what is included in the CDM Regs, then that should be sufficient.